APPLICABLE STANDARD NFPA-72 available from National Fire Protection Association, Quincey Mass. I also recommend the National Fire Alarm Code Handbood also published by NFPA - it is more user-friendly. REQUIREMENTS output: 85dBA of 10 ft (3m) temporal pattern: triple burst as follows 0.5s ON 0.5s OFF 0.5s ON 0.5s OFF 0.5s ON 1.5s OFF {repeat] NFPA-72 has more detail regarding chimes, light- and tactile signals for hearing impaired and interaction of signals from other alarms in the building. There are also requirements for connection to a control panel, tamper etc. which apply to a complete alarm system. David Sterner Alarm Device Manufacturing Co.
______________________________ Reply Separator _________________________________ Subject: Smoke Alarms Author: "Ralph Cameron" <SMTP:ral...@igs.net> at ADEMCONET List-Post: emc-pstc@listserv.ieee.org Date: 5/31/2000 3:41 PM Not sure if this is apprpriate for this group. Can anyone tell me what the audible requirements are for standard approved smoke alarms? Is there a spec for them ? Mny seniors have difficulty hearing a high pitched tone and I am attempting to determine alternatives. Thanks Ralph Cameron EMC Consultant for Suppression of Consumer Electronics (After sale) ------------------------------------------- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Jim Bacher: jim_bac...@mail.monarch.com Michael Garretson: pstc_ad...@garretson.org For policy questions, send mail to: Richard Nute: ri...@ieee.org