Kelly, UL 1950 has a D1 (more restrictive) deviation in clause 3.2.1 than IEC 950: "Where equipment is intended to be connected to a source of supply by a power supply cord, the attachment plug shall be rated no less than 125 percent of the rated current of the equipment."
We got into a tussle with UL over this about four years ago on one of my power supplies. After two weeks of discussions with them we wound up accepting their interpretation of "attachment plug" as including the wall plug itself, the AC cordage, and any IEC-320 plugs/sockets/appliance inlets between the wall outlet and the common-mode choke of the power supply. Power Dynamics and other companies make IEC-320 plugs/sockets/appliance inlets that are rated 15A by UL and CSA, and 10A by the Europeans. But the specific approvals (wall plug to cordage, IEC-320 plug/socket to cordage) at that time only went up to 16AWG wire which is rated for 13A by UL and CSA. We wound up limiting the auxiliary-output current to 9.8A, for a maximum total input current of 10A to keep UL happy. John Barnes Advisory Engineer Lexmark International ------------------------------------------- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Jim Bacher: jim_bac...@mail.monarch.com Michael Garretson: pstc_ad...@garretson.org For policy questions, send mail to: Richard Nute: ri...@ieee.org