Hi John:


>   More significantly, its resistance affects the maximum short-circuit
>   current that can flow.

This is a valid consideration with regard to safety.

Given a 6-amp maximum, 0.75 sq mm size, and 2 meters
length.

In North America, 2X rated current is the 1-minute 
operating time of a fuse or circuit-breaker.  The
maximum resistance of the power cord (assuming a
short at the load end of the cord) would be:


          120 V
   R  =  -------  =  4 ohms.
           30 A

>From the wire tables, 0.75 sq mm wire is about 0.023 
ohm/meter.

For 4 ohms resistance we would need 4/0.023 or 173
meters of wire, or a 2-wire cord of about 85 meters.

In continental Europe, using the same assumptions 
about current and operating time, the maximum 
resistance of the cord would be:


          230 V
   R  =  -------  =  7.1 ohms.
           32 A

The wire length would be 7.1/0.023 or 312 meters,
and the cord length would be 156 meters.

So, the 2-meter length restriction (0.092 ohms) 
appears not to be in consideration of the short-
circuit current.  It appears that a 0.75 sq mm
cord could be 20 meters in length (0.92 ohms) and 
still operate the overcurrent device.


Best regards,
Rich




-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        pstc_ad...@garretson.org
     Dave Heald                davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to