Hi John:
> More significantly, its resistance affects the maximum short-circuit
> current that can flow.
This is a valid consideration with regard to safety.
Given a 6-amp maximum, 0.75 sq mm size, and 2 meters
length.
In North America, 2X rated current is the 1-minute
operating time of a fuse or circuit-breaker. The
maximum resistance of the power cord (assuming a
short at the load end of the cord) would be:
120 V
R = ------- = 4 ohms.
30 A
>From the wire tables, 0.75 sq mm wire is about 0.023
ohm/meter.
For 4 ohms resistance we would need 4/0.023 or 173
meters of wire, or a 2-wire cord of about 85 meters.
In continental Europe, using the same assumptions
about current and operating time, the maximum
resistance of the cord would be:
230 V
R = ------- = 7.1 ohms.
32 A
The wire length would be 7.1/0.023 or 312 meters,
and the cord length would be 156 meters.
So, the 2-meter length restriction (0.092 ohms)
appears not to be in consideration of the short-
circuit current. It appears that a 0.75 sq mm
cord could be 20 meters in length (0.92 ohms) and
still operate the overcurrent device.
Best regards,
Rich
-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.
Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/
To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc
For help, send mail to the list administrators:
Michael Garretson: pstc_ad...@garretson.org
Dave Heald davehe...@mediaone.net
For policy questions, send mail to:
Richard Nute: ri...@ieee.org
Jim Bacher: j.bac...@ieee.org
All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.