Note I am replying to all.  What is the measurement inaccuracy associated 
with a mismatch if the transmission line is vanishingly short (relative to a
wavelength)?

----------
>From: "Pommerenke, David" <davi...@ece.umr.edu>
>To: "'Ken Javor'" <ken.ja...@emccompliance.com>, "'Ravinder Ajmani'"
<ajm...@us.ibm.com>, marti...@appliedbiosystems.com
>Cc: emc-p...@majordomo.ieee.org
>Subject: RE: Pre-amps
>Date: Fri, Nov 16, 2001, 8:10 AM
>

> Dear Ken,
>
> I am thinking you are missing something (hope that I am correct).
> If you simply shorten the cable to zero, the problem of the missmatch, and
> the effect of an error that is not corrected for by the antenna factor still
> remains.
>
> David Pommerenke
>
> -----Original Message-----
> From: Ken Javor [mailto:ken.ja...@emccompliance.com]
> Sent: Thursday, November 15, 2001 5:51 PM
> To: Pommerenke, David; 'Ravinder Ajmani'; marti...@appliedbiosystems.com
> Cc: emc-p...@majordomo.ieee.org
> Subject: Re: Pre-amps
>
>
> If input VSWR for preamp and output VSWR for antenna are both bad, then it
> seems a simple solution is to connect preamp input to antenna output and let
> 50 Ohm output of preamp drive cable, solving two problems at once.  Am I
> missing something?
>
> ----------
>>From: "Pommerenke, David" <davi...@ece.umr.edu>
>>To: "'Ravinder Ajmani'" <ajm...@us.ibm.com>, marti...@appliedbiosystems.com
>>Cc: emc-p...@majordomo.ieee.org
>>Subject: RE: Pre-amps
>>Date: Thu, Nov 15, 2001, 7:49 AM
>>
>
>>
>> On the amps:
>>
>> For emissions there are the following electrical criteria:
>>
>>  - Noise figure  expect about 4 dB for a broadband amp 30 MHz - 2 GHz.
>>    The noise figure is often larger at the lower frequencies if the
>> amplifier goes up to many GHz.
>>
>>  - Input SWR. This is important. Most broadband amps (especially if they
> go
>> up to many GHz)
>>    have a bad input match at low frequencies. As the log-per antennas have
> a
>> bad mismatch too,
>>    you will have multiple reflections on the cable between the antenna and
>> the pre-amp.
>>    This reflections will influence your measurement and cannot be
> corrected
>> for by the antenna
>>    factor. They may be as large as a few dB below 100 MHz. For that
> reason,
>> you may be forced
>>    to add a 3 dB attenuatore at the antenna. This increases your noise
>> figure by 3 dB.
>>
>>  - Gain. Of course, you need only as much gain as is needed to overcome
> the
>> cable loss (cable to
>>    the spectrum analyzer) and the noise figure of the spectrum analyzer.
>> More gain will not help
>>    you.
>>
>> David Pommerenke
>>
>> -----Original Message-----
>> From: Ravinder Ajmani [mailto:ajm...@us.ibm.com]
>> Sent: Wednesday, November 14, 2001 1:27 PM
>> To: marti...@appliedbiosystems.com
>> Cc: emc-p...@majordomo.ieee.org
>> Subject: Re: Pre-amps
>>
>>
>>
>>
>> Joe,
>> HP (Agilent) make good Pre-amps for different frequency ranges.  If you
> are
>> looking for an economical solution then you may try Com Power Corp. at
>> (949) 587-9800.
>>
>> Regards, Ravinder
>> PCB Development and Design Department
>> IBM Corporation
>> Email: ajm...@us.ibm.com
>>
> ***************************************************************************
>> Always do right.  This will gratify some people and astonish the rest.
>> .... Mark Twain
>>
>>
>>
>>
>>
>>                     MartinJP@appliedbiosyst
>>
>>                     ems.com                       To:
>> emc-p...@majordomo.ieee.org
>>                     Sent by:                      cc:
>>
>>                     owner-emc-pstc@majordom       Subject:     Pre-amps
>>
>>                     o.ieee.org
>>
>>
>>
>>
>>
>>                     11/14/2001 10:14 AM
>>
>>                     Please respond to
>>
>>                     MartinJP
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> I am having some difficulties locating manufacturers that provide preamps
>> with a 20-22dB gain.
>>
>> What manufacturer/model do you recommend? Why?
>>
>> Your assistance is appreciated.
>>
>> Regards
>>
>> Joe Martin
>> Applied Biosystems
>>
>>
>> -------------------------------------------
>> This message is from the IEEE EMC Society Product Safety
>> Technical Committee emc-pstc discussion list.
>>
>> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>>
>> To cancel your subscription, send mail to:
>>      majord...@ieee.org
>> with the single line:
>>      unsubscribe emc-pstc
>>
>> For help, send mail to the list administrators:
>>      Michael Garretson:        pstc_ad...@garretson.org
>>      Dave Heald                davehe...@mediaone.net
>>
>> For policy questions, send mail to:
>>      Richard Nute:           ri...@ieee.org
>>      Jim Bacher:             j.bac...@ieee.org
>>
>> All emc-pstc postings are archived and searchable on the web at:
>>     No longer online until our new server is brought online and the old
>> messages are imported into the new server.
>>
>>
>>
>>
>>
>> -------------------------------------------
>> This message is from the IEEE EMC Society Product Safety
>> Technical Committee emc-pstc discussion list.
>>
>> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>>
>> To cancel your subscription, send mail to:
>>      majord...@ieee.org
>> with the single line:
>>      unsubscribe emc-pstc
>>
>> For help, send mail to the list administrators:
>>      Michael Garretson:        pstc_ad...@garretson.org
>>      Dave Heald                davehe...@mediaone.net
>>
>> For policy questions, send mail to:
>>      Richard Nute:           ri...@ieee.org
>>      Jim Bacher:             j.bac...@ieee.org
>>
>> All emc-pstc postings are archived and searchable on the web at:
>>     No longer online until our new server is brought online and the old
>> messages are imported into the new server.
>>
>> -------------------------------------------
>> This message is from the IEEE EMC Society Product Safety
>> Technical Committee emc-pstc discussion list.
>>
>> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>>
>> To cancel your subscription, send mail to:
>>      majord...@ieee.org
>> with the single line:
>>      unsubscribe emc-pstc
>>
>> For help, send mail to the list administrators:
>>      Michael Garretson:        pstc_ad...@garretson.org
>>      Dave Heald                davehe...@mediaone.net
>>
>> For policy questions, send mail to:
>>      Richard Nute:           ri...@ieee.org
>>      Jim Bacher:             j.bac...@ieee.org
>>
>> All emc-pstc postings are archived and searchable on the web at:
>>     No longer online until our new server is brought online and the old
>> messages are imported into the new server.
>>
> 

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        pstc_ad...@garretson.org
     Dave Heald                davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to