According to the Belden wire table, 10awg carrying 
32 amps will produce a 35C rise above ambient. And 
according to them, the bundling factor is 1.0 for 1, 2, 
or 3 bundled wires.  If you're qualifying anything up 
around 40C high temp, your wire's going to be 75C.  

5C doesn't give you much overhead for 80C rated 
wire.  So, you might want to think long and hard about 
using 80C rated wire for such an application.  IMO, you'd 
have to start with a minimum 105C rated wire. 

8awg at 32 amps looks more like 23C rise above ambient. 