Martin

Having read several other contributors comments on your question, I have to
say that I totally agree with them (test with  the switch in both positions)
for one very practical reason.

I know of several occasions where personnel have lifted disconnected
equipment by wrapping their arms around it - and then dropped it again by
reflex when their fingers touched the pins of the plug and they got a
non-fatal shock from the charged capacitors on the plug-side of the switch. 

In one case the person suffered a badly injured foot (20-30lbs from 4feet up
make a hell of an impact on your foot), and in the other case the weight
missed the person's foot - but I then spent many hours trying to defend my
company which supplied the equipment (even though it complied with the
standard IEC380 - it was a long time ago! - and met the same requirements as
60950 does now)!

I would expect that other forum participants will be able to relate similar
incidences.

Personaly, based on the above experiences, I play safe and apply the test
whatever capacitance is across the pins with the switch open. As I said for
the second example, even capacitance at/below the compliance limit is enough
to cause the reflex action which may cause the recipient of the shock to
involuntaritarily do something which results in harm to himself (or someone
else). Given the current effects of product liability legislation I would
take any chances at all!

John Allen
Thales Defence Communications Division
Bracknell, UK

-----Original Message-----
From: marti...@appliedbiosystems.com
[mailto:marti...@appliedbiosystems.com]
Sent: 11 May 2001 17:31
To: emc-p...@majordomo.ieee.org
Subject: Capacitor Discharge Test



We evaluate our laboratory equipment to UL 3101-1, CSA 1010.1 and EN
61010-1.

Section 6.10.3  of UL 3101-1 states "If plug pins of cord-connected
equipment receive a charge from an internal capacitor, the pins shall not
be HAZARDOUS LIVE 5s after disconnection of the supply".  We have always
performed this test with the power switch in the ON position and would have
the unit running then unplug the power cord and take our reading on the
oscilloscope.  We have never measured any voltages above the HAZARDOUS LIVE
limits of 30Vrms, 42.4V peak or 60Vdc.
Our new NRTL Engineer has now also requested us to perform this test with
the power switch in the OFF position.  With the switch in the off position
our voltages after 5 seconds are close to line voltage.  The NRTL is
considering this a failure.

However, UL 3101-1 also states in Section 6.10.3 "For plugs receiving a

charge from an internal capacitor, the measurements of 6.3 are made to
establish that the levels of 6.3.1.3 are not exceeded."  6.3.1.3 requires
measuring the overall capacitance from the unit.  Our NRTL states that
there is no method available to measure the overall capacitance of the
unit.

 Has anyone else in the group had any experience with this issue?  Does
your NRTL require testing with the switch in the OFF position?  Do your
units fail with the switch in the OFF position?  Is it a failure just
because the voltage limits are exceeded, or is it only a failure if the
current and capacitance limits are exceeded. (Similar to the Permissible
Limits Requirements).  Have you had any experience with NRTL's not being
able to measure the overall capacitance?

All responses are greatly appreciated.

Regards

Joe Martin
Applied Biosystems
marti...@appliedbiosystems.com




-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        pstc_ad...@garretson.org
     Dave Heald                davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://www.rcic.com/      click on "Virtual Conference Hall,"

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        pstc_ad...@garretson.org
     Dave Heald                davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://www.rcic.com/      click on "Virtual Conference Hall,"


Reply via email to