Scott,

I have not heard of surge protection device (SPD) being a requirement for
circuit breakers, but I do know that SPDs are required to be after the main
over-current protective device of a facility as per NEC 2002, article 285
and UL 1449, regardless if the SPD contains integral fusing or not.  In
addition, per the NEC, which is clarified in an upcoming IEEE application
guide on surge protective device (PC62.72, Working Group 3.6.6), the fault
current rating of the SPD must be equal to or greater than the fault current
capability of the over-current protective device utilized in front of the
SPD.

For SPDs designed for use inside other equipment, over-current protection of
the SPD is not required as long as building over-current protection is
provided.

Surge arrestors, SPDs designed to be placed in front of the main
over-current protective device of the facility and on transformer poles, are
governed by article 280 of the NEC and UL's OWHX classification.

Bryan Cole
Director of Engineering
Product Safety Officer
Emerson Network Power - Control Concepts
Binghamton, New York 13902
Phone: 607.724.1352 extension 238
Fax:     607.724.0153
E-mail: bryan.c...@control-concepts.com
www.Liebert.com
www.Control-Concepts.com
www.Edcosurge.com


-----Original Message-----
From: Scott Barrows [mailto:sbarr...@curtis-straus.com]
Sent: Thursday, August 15, 2002 9:40 AM
To: PSTC
Subject: Circuit Breakers



Hi All,
Does anyone have any information concerning the requirement for surge
protection on circuit breakers that came into effect this June? This may
just be for the EU and Laboratory equipment.

Regards,
Scott


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to