Hi Chris,

Classified area = hazardous location = an area where the atmosphere may be
easily ignitable

Class = type of hazard; Class 1 = gas vapours; 2 = combustible dust, 3 =
ignitable fibers

Zone = Frequency of the hazard; Zone 1 means hazard present frequently or
for long periods; Zone 2 means hazard present only during maintenance or
mishap (leaky valve); Zone 0 means hazard present continuously in normal use
(the headspace above the flammable liquid in the holding tank, and the lid
of the tank)

EEx = Approved to the European version of the Ex standards

d = a protection method = 'flameproof enclosure' - "contain the explosion"
n = a protection method = 'non-incendive' - "no hot surfaces"

Gas Group IIB = Ethylene family of gases

T3 = maximum product surface temperature of 200 C, under fault conditions

Relevant authority for Europe = Notified Body (Notified to the ATEX
Directive 94/9/EC)

You scratched the surface on a really big topic; here are some links for
your education:

http://europa.eu.int/comm/enterprise/atex/index.htm - ATEX (94/9/EC) home
page, with links to harmonized standards and notified bodies
http://europa.eu.int/comm/enterprise/atex/guide/guide_en.pdf - ATEX
guideline
http://www.iecex.com/home.htm - IEC-EX home (like the CB Scheme for Ex)
http://www.ul.com/hazloc/ - UL's hazloc page
http://www.epsilon-ltd.com/ - Epsilon Ltd., home page - lots of hazloc info
http://www.extronics.com/Ex_Info/protection_concepts.html - EXTronics has a
good protection concepts table here.

You could impress the questioner by pointing out that 'EEx n' devices are
not allowed in Zone 1 areas... 

I'm guessing you have a European customer who needs a Zone 2 rating - I
don't really see network diagnostic equipment being needed in a Zone 1 or 0
location.

The full product rating would then likely be: ATEX Group 2 Category IIB, EEx
n IIB T3.

By the way, the ATEX Directive, mandatory July 1, 2003,requires notification
(certification by an ATEX Notified Body) of your quality system per
prEN13890, which is essentially ISO9000:2000 + specific ATEX requirements.
Periodic factory surviellence is mandated by the Directive (is this a
first?).

Also note that the Class/Division system of defining HAZLOCS is widely used
in North America; although the Class/Zone system has been allowed since 1999
(re 1999NEC Articles 505-510), only one facility has adopted the Class/Zone
system to date. There are three, largely separate, approvals efforts for
HAZLOC equipment; the USA, Europe, and ROW. The USA requires listing by an
OSHA-approved NRTL. Europe requires an ATEX Notification. ROW - Australia,
Brazil, Japan, among others - issue a national cert based on IEC standards.

Have fun.

Doug Massey
Lead Regulatory Engineer
LXE, Inc.

-----Original Message-----
From: Chris Maxwell [mailto:chris.maxw...@nettest.com]
Sent: Monday, July 29, 2002 10:52 AM
To: EMC-PSTC Internet Forum
Subject: Hazardous Area Designations/Certifications



Hi all,

I have been asked a question regarding the following:

"use in a Zone 1 and Zone 2 classified area. This equipment shall be
certified EEX d and EEx n by a relevant authority (e.g. BASEEFA, CENELEC
etc.) and shall be suitable for Gas Group IIB and Temperature Class T3."

Can anyone elaborate on the above information?  What standard defines "Zone
1" or "Zone 2"?  What standard defines "EEX d" and "EEX n"?  What about "Gas
Group IIB" and "Temperature Class T3?"

Any clarification, elaboration, elucidation and/or explanation that the
group members could provide would certainly be appreciated.

Thanks,

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 





-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to