Hi Lauren,

You didn't provide sufficient information regarding the application so I can't 
say much about tagout.

As for lockout:
29 CFR 1910.147 The control of hazardous energy (lockout/tagout) pretty clearly 
rules out performing lockout by locking a cover.

Lockout is defined as
"The placement of a lockout device on an energy isolating device, in accordance 
with an established procedure, ensuring that the energy isolating device and 
the equipment being controlled cannot be operated until the lockout device is 
removed."

A lockout device is defined as
A device that utilizes a positive means such as a lock, either key or 
combination type, to hold an energy isolating device in the safe position and 
prevent the energizing of a machine or equipment. 

A breaker panel cover is not a lockout device applied to an energy isolating 
device.  It does not "hold the energy isolating device in the safe position".

Under certain circumstances I can see where locking the cover might provide 
"equivalent protection" as required for a tagout approach.  Under other 
circumstances (remote closing, lockout locks not individually assigned) it 
might be inviting an accidental electrocution or startup.  For this reason, the 
method you propose is installation specific.

Additionally, I fail to see the need for such a method, as since 1990 it is 
required that "whenever replacement or major repair, renovation or modification 
of a machine or equipment is performed, and whenever new machines or equipment 
are installed, energy isolating devices for such machine or equipment shall be 
designed to accept a lockout device".

Regards,

Matthew Meehan

PS Gruss an FP


Original Message       processed by Tobit InfoCenter 
Subject: Breaker panel lockout-tagout (18-Sep-2002 19:29)
From:    lcr...@tuvam.com
To:      m...@huber-online.com


Group, 
Is anyone aware of an authoritative position on the acceptability (or not) of 
applying a lock to a breaker panel cover (and so affecting access to other, 
unrelated, breakers behind the same cove) to achieve OSHA compliant 
Lockout/Tagout rather than applying the lock to breaker directly?
-Lauren Crane 
TUV America 