In a message dated 10/8/2002, Alex McNeil writes:

> As I am in panic mode, is there some guidance out there for me e.g. is it
> usually a matter of changing the interface IC's or hanging special
> components onto the lines?
> 


Hi Alex:

This test is indeed a difficult one to pass, but in general the 
transformer-type interfaces that you are dealing with are less susceptible 
than some other types.  I have seen ISDN and Ethernet interfaces pass this 
test without the need for extreme measures.  In the absence of more specific 
information about your situation, I can offer just a few general guidelines:

1) EN 55024 allows you to use either a CDN or a clamp to induce the RF.  Some 
people find that they get more favorable results with the clamp than with the 
CDN.

2) The interference is applied common mode.  In *theory* your transformer 
coupled interfaces will have fairly good common mode rejection, but this can 
be compromised by a bad layout or by some types of surge protection devices.

3) If you have to add some filtering to pass, adding a common mode choke is a 
good first step toward reducing susceptibility.  Adding caps from each 
conductor to chassis ground also helps, especially if used in conjunction 
with a common mode choke, with the choke on the line side of the caps.  Note, 
however, that high value caps can interfere with proper operation of the 
circuit.



Joe Randolph