I can't verify the part that after a wrench was dropped on the -48V bus
bars, all the other equipment was blown, but I can throw a little light
on this. The previous company I worked for made Telco rectifiers. Our
largest system had an output of over half a megawatt (!) at -48V. The
bus bars were not little 1" diameter rods, but laminated copper bars
that were 6" x 4" in cross section. One customer was worried about what
would happen when ol' "Bubba" dropped his wrench across the bars, and I
had to prove that the bars would not tear themselves loose due to the
repulsive force caused by peak short circuit current from the batteries
being charged by the rectifier system. The current was not
insubstantial: 100,000 Amps would flow for about 15mS before the fuse
cleared. It was assumed that not only would Bubba's wrench vapourize,
but so would Bubba.

Bob Wilson
TIR Systems Ltd.
Vancouver.

-----Original Message-----
From: Robert Macy [mailto:m...@california.com] 
Sent: February 25, 2002 10:34 PM
To: Jim Bacher; ieee pstc list
Subject: Re: Use of PCB Traces as Fuse and Voltage suppressor


Jim,

You touch on an important issue concerning a fuse - just how does it
"blow"?

Years ago I discovered by accident that fuses were designed with some
remarkable properties, when we had to make our own transient generator
to
verify some telcom equipment's compliance to a BABT power supply
transient
spec.

The BABT spec required that you simulate some very husky power
transients.
It was like a short occurs in adjacent electronics followed by the
inductive
kick.  The -48 voltage would clamp to around 10 volts then "pop" up to
over
300 volts capable of supplying 500A for something like more than 50mS.
If
you didn't design your protection properly you would have a lot of
unintentional PCB trace fuses.  [  Actually heard that the spec
originated
because a workman had dropped his wrench across the 1 inch diameter rods
which supply the -48 to the telco building from the battery building.
After
the wrench evaporated, they found the whole room of equipment was blown,
thus the spec.  Somebody verify that?  ]

The simulator used 4 deep discharge current vehicle batteries supplying
the
telcom equipment through 50uH of inductance (that was 0000 cable on a
spool).  Parallel to that you used a starter solenoid to short out a
fuse
with a dead short.  Amazingly the larger fuses never produced much kick
back.  They were designed to blow gently away.  Tried all kinds.  Most
of
the 8AG didn't do much, other types, nothing, even the 100 amp cartridge
types, nothing,  The absolute best was a 1A 8AG type.  When that went,
you'd
get a flash of light, 300 volts trying to drive 500 amps into
everything,
and even the coil would "jump" up off the floor.

Talk about PCB traces acting like fuses.

Anyway, I learned a respect for people who design fuses to make them go
away
so gently when there is an incredible potential for some extremely high
voltage transients.

                           - Robert -

       Robert A. Macy, PE    m...@california.com
       408 286 3985              fx 408 297 9121
       AJM International Electronics Consultants
       619 North First St,   San Jose, CA  95112



-----Original Message-----
From: Jim Bacher <jim.bac...@paxar.com>
To: 'Cortland Richmond' <72146....@compuserve.com>; Chris Maxwell
<chris.maxw...@nettest.com>; ieee pstc list <emc-p...@ieee.org>
List-Post: emc-pstc@listserv.ieee.org
Date: Monday, February 25, 2002 3:04 PM
Subject: RE: Use of PCB Traces as Fuse and Voltage suppressor


>
>Long time ago we found that the traces worked well as fuses when the
>batteries were fully charged. However, when the batteries were mostly
>discharged, the PC Board traces did not work well as fuses. At lower
battery
>charge levels, the traces became very hot and ignited the PC Board
rather
>than opening the traces up.  I therefore would recommend against using
PC
>Board traces as fuses.
>
>
>Jim
>
>Jim Bacher,  Senior Engineer
>Paxar Corp.
>e-mail: jim.bac...@paxar.com  or  j.bac...@ieee.org
>voice: 1-937-865-2020
>fax: 1-937-865-2048
>
>-----Original Message-----
>From: Cortland Richmond [mailto:72146....@compuserve.com]
>Sent: Thursday, February 21, 2002 12:53 AM
>To: Chris Maxwell; ieee pstc list
>Subject: RE: Use of PCB Traces as Fuse and Voltage suppressor
>
>
>
>When do you need a fuse? Level II is the only time you are allowed to
lose
>functionality, and the requirement for THAT is, it can't catch fire or
>explode. I've seen "trace fuses" tried. The problem comes after the
trace
>blows.  You are at the mercy of your board shop, and if you use a
number of
>them, results might not be all that repeatable.  AS i said earlier,
I've
>had a board catch fire in my hand (though not as a result  of stress,
but a
>solder splash). It is instructive.
>
>Cortland
>
>-------------------------------------------
>This message is from the IEEE EMC Society Product Safety
>Technical Committee emc-pstc discussion list.
>
>Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>
>To cancel your subscription, send mail to:
>     majord...@ieee.org
>with the single line:
>     unsubscribe emc-pstc
>
>For help, send mail to the list administrators:
>     Ron Pickard:              emc-p...@hypercom.com
>     Dave Heald:               davehe...@mediaone.net
>
>For policy questions, send mail to:
>     Richard Nute:           ri...@ieee.org
>     Jim Bacher:             j.bac...@ieee.org
>
>All emc-pstc postings are archived and searchable on the web at:
>    http://ieeepstc.mindcruiser.com/
>    Click on "browse" and then "emc-pstc mailing list"


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to