Sam, Section 5 of EN61000-3-2 lists examples of the environments and a partial listing include houses, shops, offices, cinemas, bars, and workshops. An industrial device that is intended to be used in both an industrial location (i.e., not from the public distribution grid) and in a cinema, for example, would have to comply with EN61000-3-2. Products intended solely for industrial locations and not powered from the public distribution grid (i.e. the grid that powers the listed locations above) do not have to comply with this standard. Richard Woods Sensormatic Electronics Tyco International
From: Sam Wismer [mailto:swis...@acstestlab.com] Sent: Wednesday, January 29, 2003 2:43 PM To: EMC Forum Subject: EN61000-3-2/3 applicability The scope of these standards includes all equipment having an input current upto and including 16A per phase and intended to be connected to a public low-voltage distribution systems of between 220V and 250V at 50Hz line to neutral. Does public infer that only consumer goods that use residential service are obligated to these standards or are industrial products used in industrial locations that meet the electrical specifications as identified above also obligated to these standards? Kind Regards, Sam Wismer Engineering Manager ACS, Inc. *Tel: (770) 831-8048 *Fax: (770) 831-8598 *Web: <http://www.acstestlab.com> www.acstestlab.com <mailto:*swis...@acstestlab.com> *swis...@acstestlab.com