Jim, Ken, is correct in that when MOV's fail, they fail short. That is why
you see a circuit breaker or fuse in front of the MOV's. If your safety
ground is defective or does not return to the neutral side of the power
source, then your safety ground raises to line potential when the MOV's
short line to safety ground, with significant current available. In a case
like this the failure does not trip the circuit breakers or fuses in the
electrical panel. 

We had a such a failure here (multiple failures were to blame) and the only
thing damaged were 26 MOVs (in 26 electrical strips) that were line to
safety ground. None of the computers plugged into the strips were damaged,
even though fuses blew to protect the MOVs (after letting the smoke out of
the MOVs), but left the computers powered up. None of the computers had MOVs
line to safety ground. In our case the cubical area is three phase (115VAC
60Hz). One cubical was miss wired, which put the neutral to safety ground
MOV in the none fused part of the electrical strip, in to the line side of
the circuit. The main electrical box for the area was not properly grounded,
nor was the safety ground tied to the neutrals. So when the MOV failed it
raised the safety ground to the line potential of phase A, which put 230VAC
across all the MOV's on Phase B and Phase C. As Murphy would have it the MOV
that failed had a unintentional heatsink and survived longer than it should
have.  All the other MOV's did not have heatsinks.

The reality is you should never really need a MOV from line to safety ground
(or neutral to safety ground). It is the difference in potential that
destroys semiconductors. In most designs the semiconductors are line to
neutral not line to ground. So as long as you have one across line to
neutral you should be OK (not to mention the filters that assist).

The past discussions on this subject can be found in our archive on :
https://www.ieeecommunities.org/emc-pstc?go=t907166

Jim

Jim Bacher,  Senior Engineer
Paxar Americas, Inc.
e-mail: j.bac...@ieee.org
 


From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Ken Javor
Sent: Thursday, December 11, 2003 11:08 PM
To: Jim Eichner; 'EMC-PSTC - forum'
Subject: Re: MOV's to ground



Not a legal answer, but I have seen a failure mode for MOVs where they
partially conduct line current.  This was in power strips.  My house
electrical system took a lightning hit.  Nothing was damaged but the MOVs,
including all the stuff in the house not connected to MOV "protected" power
strips.  The power strips with bad MOVs were quite hot (thermally) due to
the "fault current" (high impedance short to ground).  The MOVs were tiny, I
think larger ones might have fared better.  No doubt there is a spec
covering how many Joules/Watts an MOV must be able to absorb without damage.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com