I suggest that the inductive component of the mains impedance is a large
contributor to the variation in harmonic amplitude measurement.  It may
help to specify the real and imag components of that impedance in the
testing standard.  (e.g.. an AC voltage source with a known impedance in
series)

Ralph McDiarmid, AScT 
Compliance Engineering Group 
Xantrex Technology Inc.


From: [email protected] [mailto:[email protected]] On Behalf
Of John Woodgate
Sent: July 19, 2005 7:28 AM
To: [email protected]
Subject: 'Variability' of some EMC test results

IEC/EN 61000-3-2 sets limits for mains harmonic current emissions up to
the 40th harmonic. It has been a 'standard result' for a long time that
for single-phase rectifiers with capacitive filters, the harmonic
spectrum has nulls or quasi-nulls, depending on the 'conduction angle' 
of the rectifier diode(s). (The conduction angle is the fraction of the
half-cycle during which the diode(s) conduct(s), expressed as an angle.)

For example, a simplified theoretical analysis of the spectrum for a
full-wave (bi-phase) rectifier with 60 degrees conduction angle shows
zero amplitude for the 9th, 15th, 21st, 27th... every triplen harmonic
of order 9 or greater. For 55 degrees conduction angle, the amplitudes
of the 17th, 23rd and 29th harmonics are small but not zero, and the
15th and higher triplen harmonics are far from zero amplitude.

The conduction angle is dependent on the supply voltage, the load
current, the filter capacitor value, the values (real and imaginary) of
any impedance in series with the rectifier, including the source
impedance of the mains supply, and the temperatures of some components,
notably the diodes, of course. The combined effect of all these may me
such that the results of two measurements of the same equipment, even
with the same test equipment at different times, may differ in detail
significantly.

For people beginning to become accustomed to 'uncertainty' estimates of
a few dB, this effect is disconcerting, and needs to be explained. The
subject was brought to the attention of the IEC by the German regulatory
authorities, through the German National Committee of the IEC. After
some investigation, the principle  was established (I hope: the dust
hasn't quite settled yet!) that what matters is whether any of the
results show that a limit is violated: for the cases where 'variability'

is known to occur, differences between test results that do not involve
any violation of a limit should not be considered a cause for concern.

If this thread runs a bit, I will put some relevant Word documents on an
unlinked page on my web site.
--
Regards, John Woodgate, OOO - Own Opinions Only.
Deadlines are 90% of deadliness.
http://www.jmwa.demon.co.uk Also see http://www.isce.org.uk


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             [email protected]
     Mike Cantwell            [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             [email protected]
     Mike Cantwell            [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to