[email protected] wrote (in <of8b335021.11530a0d-on8625704b.00520ace-8625704b.00532...@mmm.com>) about 'Flicker and dmax Changes Caused by Manual Switching', on Wed, 27 Jul 2005: >Is there value to this test if you are powering your equipment from a >separate power source and not directly from the power lines? In our lab >(US) we get our 230 vac, 50 Hz from a separate power generator and line >conditioner that I suspect has different regulation then the public >lines. The dmax that we see is the dmax from our generator. Or is my >thinking wrong?
No, you are correct. But I suspect you don't have the standard, which you really should have, because it specifies the necessary reference impedance, 0.4 + j0.25 ohms for single phase equipment. If you know the real and imaginary parts of the impedance of your generator, you can calculate the result that would be obtained with the reference impedance. -- Regards, John Woodgate, OOO - Own Opinions Only. Deadlines are 90% of deadliness. http://www.jmwa.demon.co.uk Also see http://www.isce.org.uk This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. Website: http://www.ieee-pses.org/ To post a message to the list, send your e-mail to [email protected] Instructions: http://listserv.ieee.org/listserv/request/user-guide.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas [email protected] Mike Cantwell [email protected] For policy questions, send mail to: Richard Nute: [email protected] Jim Bacher: [email protected] All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstc