Jim,

Your not going to find a single statement that says all breakers must have
interrupt ratings at least 5000 A.  The requirement is embedded in the NRTL
Listing of the circuit breaker.  "Supps" are not Listed.

You will find the following hints:  110.2  "Approval - The conductors and
equipment required or permitted by this Code shall be accepted only if
approved".  By this, you can only use Listed circuit breakers.  Here is the
link to UL's General Guide Info for Molded-Cased Circuit breakers and
circuit-breaker enclosures.  Note that there is a marking requirement for
breakers with an interrupt rating  greater than 5000 A, because 5000 A is
the minimum rating in accordance with UL 489:

http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name
=DIVQ.GuideInfo&ccnshorttitle=Circuit+Breakers,+Molded-case+and+Circuit+Brea
ker+Enclosures&objid=1074081597&cfgid=1073741824&version=versionless&parent_
id=1073985604&sequence=1

You might want to refer to 110.9 "Interrupt rating", and 240.83(C) of the
2005 NEC Handbook (because the blue-print has useful information) concerning
interrupt rating markings on circuit breakers.

Now, concerning supplementary protectors, remember 110.2 above?  There is no
Listing category for supplementary protectors!  They are UL Recognized,
which means that they can only be used as internal protection for Listed
appliances.  They do not generally have 5000 A interrupt capability.  Here
is the link to the General Guide for supplementary protectors:


http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name
=QVNU2.GuideInfo&ccnshorttitle=Protectors,+Supplementary+-+Component&objid=1
073793222&cfgid=1073741824&version=versionless&parent_id=1073793221&sequence
=1

The guide says that supplementary protectors are not intended to provide
branch circuit overcurrent protection required by ANSI/NFPA 70, "National
Electrical Code".

Hope this helps,


Don Gies, N.C.E
Senior Product Compliance Engineer
Lucent Technologies
Holmdel, NJ 07733 USA



From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: Monday, September 19, 2005 8:07 PM
To: EMC-PSTC@listserv.ieee.org
Subject: Protectors vs breakers in the NEC


I'm sure it's in there...somewhere.

I'm looking for where the NEC (2005 please) says that the overcurrent
protection provided for branch circuits has to be a circuit breaker with
an interrupt rating of at least X (I believe it's 5000A), as opposed to
a supplemental protector.  The closest thing I can find is...

110.9 Interrupting Rating.

Equipment intended to interrupt current at fault levels shall have an
interrupting rating sufficient for the nominal circuit voltage and the
current that is available at the line terminals of the equipment.

This doesn't really say it.  It suggests that if I could go buy a
supplemental protector rated for say 500A interrupt and if I could
convince the electrical inspector that at the location where it will be
installed (say in a sub-panel at the end of a long run of No. 14AWG
wire) that's all the fault current available, then that would be ok?!

I thought they had to be "real" circuit breakers AND they had to have
appropriate interrupt ratings.  Yes?  No?

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com
Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-
   2005 IEEE Symposium on Product Safety Engineering
             3-4 October   Schaumburg, IL
          http://www.ieee-pses.org/symposium


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             emcp...@ptcnh.net
     Mike Cantwell            mcantw...@ieee.org

For policy questions, send mail to:

     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

-
   2005 IEEE Symposium on Product Safety Engineering
             3-4 October   Schaumburg, IL
          http://www.ieee-pses.org/symposium


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             emcp...@ptcnh.net
     Mike Cantwell            mcantw...@ieee.org

For policy questions, send mail to:

     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to