Hi Chris,

I'd just like to add a few words since I have experience which is counter to
some of the opinions posted.

First, if shields didn't work, we would never used them... Right?

Second, the effectiveness of a shield depends on several factors including the
nature of the noise source, the nature of the victim and the shield chosen.

Third, employing some shield topologies could introduce undesirable side
effects like ground loops. This is really a problem for Audio, and not really
an Ethernet issue unless you go long distances. If you do, then go optical.

Fourth, incorrect opinions are formed because of some unknown action when
something was tried.

Fifth, too much credence is given to what SHOULD happen in a perfect world...


So, here are my specific comments on Ethernet in a noisy environment:

We have tested many insitu machines with Ethernet. Without an exception the
machines having shielded cables had less noise issues.

We have, in the lab, tested many vendors Ethernet products. A significant
number performed better with shielded cables. This included routers from
Cisco, Belden and Netgear that came in as support equipment. The two
exceptions were Ethernet to RS-232 and RS-485 converters.

For my main client when testing his products, shielded Ethernet rarely caused
issues, even performing EFT testing at 4 kV. Issues observed were almost
always the PC locking up though noise getting in via the keyboard or mouse
cables.

In the lab we used to have an unshielded network. This would trash every time
EFT was performed. We now use a good quality Shielded Ethernet cable and have
not had one event in 4 years. I have not seen issues with ground loops...

Sincerely,

Derek Walton
L F Research



-----Original Message-----
From: Chris Wells <radioactive55...@comcast.net>
To: EMC-PSTC@LISTSERV.IEEE.ORG
Cc: christopherdwe...@eaton.com
Sent: Sun, Nov 28, 2010 7:48 pm
Subject: RE: [PSES] Shield bonding on STP Cat5 Ethernet cables


Thanks all


I've received some good feedback on this topic.


Seems that most of you don't see a lot of value in SHIELDED - STP Cat 5


cable over well balanced UTP.  I understand the value of a balanced cable


and how it leads to a solid CMRR.  At the same time I have seen shielded


cable make a difference with those RS485 applications so I am not letting go


yet.





The power distribution gear I am talking about will include Motor Control


Centers with Adjustable Speed Drives and Soft starts.  Also Lighting supply


panels feeding electronic Ballasts and a variety of interesting loads found


in Commercial and Industrial applications.  All sorts of continuous diode


commutations driving current pulses and then a variety of surge and fault


events that happen less frequently.  We typically test our equipment to


level 3-4 for the standard array of IEC61000-4-X tests.





I did point out that we presently try to use STP only in locally well bonded


power distribution line ups.  I would not expect that there would be any


significant ground loops between local nodes.  Under those restrictions do


you still think STP is not useful?





The assembly gear has little room for special Panduit or conduit chasses for


specialized Ethernet communications.  Our RS485 serial communication cables


are typically strapped to control cables with ratings up to 600V.  Belden


cable company has developed some 600V AWM STP cables which have either a


Beldfoil shield or a combination Beldfoil and 70% TC braid shield on top of


their very balanced cable.  AWM stands for Appliance Wire by Manufacture and


is basically a UL recognition that needs to be evaluated in the assembly


gear for approval.  This would allow us to strap the STP Cat5 cable to the


control bundles like our RS485 applications.





I do not know if the STP nature of the cable helps in achieving the 600V AWM


rating or not.  It may be possible to achieve this rating without the


shield, I will check.





Chris Wells


Eaton Corp.




















-----Original Message-----


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org <mailto:emc-p...@ieee.org?>
] On Behalf Of o. laney


Sent: Thursday, November 25, 2010 12:34 PM


To: j...@jmwa.demon.co.uk


Cc: EMC-PSTC@LISTSERV.IEEE.ORG


Subject: Re: [PSES] Shield bonding on STP Cat5 Ethernet cables





A magnetic field will couple through the shield even if grounded at both


ends, albeit in attenuated form.  It's really just a matter of how much


attenuation can be achieved.  I've been working on an instrument with a


pulsed magnetic field powerful enough to cause robust electrostimulation


of any flesh in the near vicinity.  An interposed sheet of ordinary


kitchen grade aluminum foil reduces but does not eliminate the shock


sensation.  This is at 5 KHz.  Turning to the matter of audio cables, hum


levels even 60 to 80 dB below the program content will prove annoying,


and the standard braided shield or even braid over foil can reduce the


hum, but at power frequencies the answer is never as much as one would


wish for.  Absent resort to mu-metal shielding, the key to audio hum


rejection is, as always, balance rather than shielding per se.





The physics is straightforward enough.  In magnetically transparent


metals such as aluminum or copper, magnetic shielding is achieved by eddy


current effect rather than flux shunting.  Most shields are rather too


thin to be efficient at this for power frequencies.  For instance, the


skin depth for pure copper at 60 Hz is around 8.5mm.  It takes 4 skin


depths to reduce ambient magnetic fields by 70 dB, easy at RF but rather


impractical for hum reduction in an audio cable routed past a power


transformer, or control wiring routed near 'cabling carrying large


currents'.  





I completely agree that UTP is satisfactory for ethernet even in noisy


industrial environments.  It's not just that the system is well balanced,


but also that the signals are transformer coupled and galvanically


isolated from the equipment with insulation good past a kilovolt.  Adding


a shield is just a means to violate galvanic isolation.  At RF a properly


grounded shield can help suppress CM radiation, but if that is a problem


then the balance assumption has been blown and ferrites are probably a


better solution.  Why are  shielded CAT-5 cables available?  Because


people are willing to buy them, and to keep EMC consultants busy when it


doesn't help.





Orin Laney








On Wed, 24 Nov 2010 21:34:10 +0000 John Woodgate <j...@jmwa.demon.co.uk>


writes:


> In message 


> <FCA549BE3ECF9D4CB8CB8576837EA4890A7744@ZEUS.cetest.local>, 


> dated Wed, 24 Nov 2010, "ce-test, qualified testing bv - Gert 


> Gremmen" 


> <g.grem...@cetest.nl> writes:


> 


> >Magnetic fields from will couple 


> >through the shield.


> 


> Well, not if it's grounded at all frequencies at both ends, but then 


> you 


> get all the circulating currents problems.


> 


> We all seem to agree - use UTP unless you find you can't, but using 


> STP 


> may be difficult anyway.


> -- 


> OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and 


> www.isce.org.uk


> John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK


> If at first you don't succeed, delegate.


> But I support unbloated email http://www.asciiribbon.org/


> 


> -


> ----------------------------------------------------------------


> This message is from the IEEE Product Safety Engineering Society 


> emc-pstc discussion list. To post a message to the list, send your 


> e-mail to <emc-p...@ieee.org>


> 


> All emc-pstc postings are archived and searchable on the web at:


> http://product-compliance.oc.ieee.org/


> Graphics (in well-used formats), large files, etc. can be posted to 


> that URL.


> 


> Website:  http://www.ieee-pses.org/


> Instructions:  http://listserv.ieee.org/request/user-guide.html


> List rules: http://www.ieee-pses.org/listrules.html


> 


> For help, send mail to the list administrators:


> Scott Douglas <emcp...@radiusnorth.net>


> Mike Cantwell <mcantw...@ieee.org>


> 


> For policy questions, send mail to:


> Jim Bacher:  <j.bac...@ieee.org>


> David Heald: <dhe...@gmail.com>


> 


> 


 





-


----------------------------------------------------------------


This message is from the IEEE Product Safety Engineering Society emc-pstc


discussion list. To post a message to the list, send your e-mail to


<emc-p...@ieee.org>





All emc-pstc postings are archived and searchable on the web at:


http://product-compliance.oc.ieee.org/


Graphics (in well-used formats), large files, etc. can be posted to that


URL.





Website:  http://www.ieee-pses.org/


Instructions:  http://listserv.ieee.org/request/user-guide.html


List rules: http://www.ieee-pses.org/listrules.html





For help, send mail to the list administrators:


Scott Douglas <emcp...@radiusnorth.net>


Mike Cantwell <mcantw...@ieee.org>





For policy questions, send mail to:


Jim Bacher:  <j.bac...@ieee.org>


David Heald: <dhe...@gmail.com>





-


----------------------------------------------------------------


This message is from the IEEE Product Safety Engineering Society emc-pstc 


discussion list. To post a message to the list, send your e-mail to 


<emc-p...@ieee.org>





All emc-pstc postings are archived and searchable on the web at:


http://product-compliance.oc.ieee.org/


Graphics (in well-used formats), large files, etc. can be posted to that URL.





Website:  http://www.ieee-pses.org/


Instructions:  http://listserv.ieee.org/request/user-guide.html


List rules: http://www.ieee-pses.org/listrules.html





For help, send mail to the list administrators:


Scott Douglas <emcp...@radiusnorth.net>


Mike Cantwell <mcantw...@ieee.org>





For policy questions, send mail to:


Jim Bacher:  <j.bac...@ieee.org>


David Heald: <dhe...@gmail.com>



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net>
Mike Cantwell <mcantw...@ieee.org> 

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 


Reply via email to