Hello Scott,
 
If you are using an NRTL approved cord, it should already have been properly
tested.  The standard used for the cord will depend on the connectrors, cord
type and countries of use.
 
UL 817 is the standard for cord sets in the United States and it does not give
a specific maximum allowable impedance for the ground connection.  It only
requires that the ground continuity be verified.  It would be difficult for a
standard to specify the ground impedance.  UL 817 covers all cord sets and
power supply cords.  This includes extension cords that can be 30 meters or
more in length.
 
EN 50116 takes into account the fact that there could be a long cord with a
higher impedance for the ground connection.  It states that when performing
routine production testing on ITE, you can inlcude the power cord in the test.
 If the result exceeds 0.1 Ohms, the impedance of the power cord can be
subtracted from the 

--- On Fri, 8/15/08, Scott Xe <scott...@gmail.com> wrote:


        From: Scott Xe <scott...@gmail.com>
        Subject: Mains cord set
        To: emc-p...@ieee.org
        Date: Friday, August 15, 2008, 8:42 AM
        
        

        I have read the safety standards for the requirement about earth 
continuity
test on finished product without mains cord.  What about the earth continuity
test for mains cord set?  For example, IEC 320 C13 connector to UK main plug
or Schuko plug.  Is there any standard for this parameter?

         

        Thanks,

         

        Scott
        - ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 
        To post a message to the list, send your e-mail to emc-p...@ieee.org 
        Instructions: http://listserv.ieee.org/request/user-guide.html 
        List rules: http://www.ieee-pses.org/listrules.html 
        For help, send mail to the list administrators: 
        Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 
        For policy questions, send mail to: 
        Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 
        All emc-pstc postings are archived and searchable on the web at: 
        http://www.ieeecommunities.org/emc-pstc 

        - ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

        To post a message to the list, send your e-mail to emc-p...@ieee.org 

        Instructions: http://listserv.ieee.org/request/user-guide.html 

        List rules: http://www.ieee-pses.org/listrules.html 

        For help, send mail to the list administrators: 

        Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 

        For policy questions, send mail to: 

        Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 

        All emc-pstc postings are archived and searchable on the web at: 

        http://www.ieeecommunities.org/emc-pstc 


Reply via email to