Other Brian,
Can you cite which clauses of which standards say In North America the power 
cord and connectors must be sized to be protected by the Branch Circuit Breaker 
but in Europe they can be protected by the downstream supplementary protector?

I was looking for that the other day.
Thanks
-Dave

From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Friday, August 08, 2014 8:26 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] FW: IEC 62368-1 rated AC input connector amperage differs 
from North America

Chuck, the rating on the product should be the max steady state current. The 
NEC requires the plug to be rated 125% of the max continuous current, which 
depending on the product can be significantly less. You can put both ratings on 
your product if you want.

In North America the power cord and connectors must be sized to be protected by 
the Branch Circuit Breaker but in Europe they can be protected by the 
downstream supplementary protector.

The Other Brian

Sent via the Samsung GALAXY S(r)4, an AT&T 4G LTE smartphone

-------- Original message --------
From: Chuck McDowell
Date:08/08/2014 4:37 PM (GMT-05:00)
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: [PSES] FW: IEC 62368-1 rated AC input connector amperage differs from 
North America

Dear Colleagues,

Does EN/IEC 60065 and/or EN/IEC 62368-1 allow  product marking a AC input to 
use rating 250V~, 32A when the appliance coupler AC rating is 250V~, 32A  
rating by VDE license? I plan to use a IEC 60309 style 250V~ 32A  Plug 
connector with appropriate cordage. This is single phase Line, Neutral, Earth 
cabling. Summary for the EU 32 plug with 32 Inlet = 32A rated input.

The USA and Canadian versions of IEC 60065 require a cord connector at 125% of 
the inlet rating so we are re-rating the product to 24A using a NEMA L6-30 Plug 
(30A plug). The same inlet from above is rated 32A USA and 30A Canada.

Will agencies sign-off on a dual AC Input current rating such as:
100-250V~
50-60Hz
24A rated cNRTLus Listed
32A rated EN/IEC Certified

Any suggestions of the correct text to use would be gladly accepted.

Respectfully,

Chuck McDowell




NOTICE: This email may contain confidential information. Please see 
http://www.meyersound.com/confidential/ for our complete policy.      -
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net<mailto:emcp...@radiusnorth.net>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net<mailto:emcp...@radiusnorth.net>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to