Hi Charlie,
Please note that Annex I for both Directives lists the essential requirements. Annex I makes no mention of declarations of conformity (DOCs). Again, the article addressing DOCs in each directive has not been identified with a delayed application. Also, there is no essential requirement in the old directives that are contradicted in the new directives. Hence, a product declared compliant to the new directives is automatically compliant with the old soon-to-be-repealed directives.

By the way, updates to the essential requirements are minor and actually provide more information.

 * EMC Directive 2014/30/EU Annex I reduces the description of fixed
   installation requirements to the first sentence of what was in the
   old Directive 2004/108/EC Annex I section 2:  "A fixed installation
   shall be installed applying good engineering practices and
   respecting the information on the intended use of its components,
   with a view to meeting the essential requirements set out in point
   1."  The old Directive 2004/108/EC Annex I section 2 also adds
   "Those good engineering practices shall be documented and the
   documentation shall be held by the person(s) responsible at the
   disposal of the relevant national authorities for inspection
purposes for as long as the fixed installation is in operation." This is really not appropriate to be listed as an EMC essential
   requirement.  The new EMC Directive 2014/30/EU correctly moves this
   statement to the last paragraph of Article 19 section 1 because
   Article 19 is a whole article discussing the requirements unique to
   fixed installations.  Please note that other electrical equipment
   that are not fixed installations also have records retention
   requirements, and those records retention requirements were never
   listed in the essential requirements.
 * Low Voltage Directive 2014/30/EU Annex I removes from the essential
   requirements one requirement that was in the old Directive
   2006/95/EC Annex I section 1(c):  "The brand name or the trade mark
   should be clearly printed on the electrical equipment or, where that
   is not possible, on the packaging." However, the new Low Voltage
   Directive 2014/30/EU still addresses this requirement but places
   this requirement in Article 6 section 6:  "Manufacturers shall
   indicate on the electrical equipment their name, registered trade
   name or registered trade mark and the postal address at which they
   can be contracted or, where that is not possible, on its packaging
   or in a document accompanying the electrical equipment."


Again, if you comply with the new directives of 2014, then you also comply with the old soon-to-be-repealed directives.

Please provide an official European Union (EU) document that confirms that "Declarations against these new Directives cannot be issued until 20 April 2016 as they have no legal standing until then."

Monrad
Note: All opinions written above are my own and are not necessarily those of any company I work for.
<http://www.oracle.com>
On 3/23/2015 3:50 PM, Charlie Blackham wrote:

Monrad

These directives cannot be used at the moment – the relevant detail is at the end of the quoted articles (with my bold text)

/2014/30/EU Article 46 /

*Entry into force and application *

This Directive shall enter into force on the twentieth day following that of its publication in the /Official Journal of the European Union/.EN 29.3.2014 Official Journal of the European Union L 96/95

Article 1, Article 2, points (1) to (8) of Article 3(1), Article 3(2), Article 5(2) and (3), Article 6, Article 13, Article 19(3) *and Annex I shall apply from 20 April 2016.*

//

2014/35/EU /Article 28 /

*Entry into force *

This Directive shall enter into force on the twentieth day following that of its publication in the /Official Journal of the European Union/.

Article 1, the second paragraph of Article 3, Article 5, Article 13(2) and (3) *and Annexes I, V and VI shall apply from 20 April 2016*.

Declarations against these new Directives cannot be issued until 20 April 2016 as they have no legal standing until then

Regards

Charlie

*From:*Monrad Monsen [mailto:[email protected]]
*Sent:* 23 March 2015 21:25
*To:* [email protected]
*Subject:* Re: [PSES] Harmonised Standards for EMC Directive 2014/30/EU and Low Voltage Directive 2014/35/EU

Hi John,
Where is it written that "Directives aren't valid until ALL member states have implemented them"?

*_ENTER INTO FORCE_*
I note that both the Low Voltage Directive and the EMC Directive clearly states: "This directive *_shall_* enter into force on the twentieth day following that of its publication in the Official Journal of the European Union." (Emphasis on "shall" is mine.) See the citations below:

  * Article 45 of the EMC Directive 2014/30/EU that was published in
    the Official Journal on 29 March 2014. Accordingly, the EMC
    Directive 2014/30/EU entered into force on 18 April 2014. Please
    also note that Article 45 does not list Article 15 (EU declaration
    of conformity) as one of the articles that has a delayed application.
  * Article 28 of the Low Voltage Directive 2014/35/EU that was
    published in the Official Journal on 29 March 2014. Accordingly,
    the Low Voltage Directive 2014/35/EU entered into force on 18
    April 2014.  Please also note that Article 28 does not list
    Article 15 (EU declaration of conformity) as one of the articles
    that has a delayed application.

As written, it appears that the new directives are entered into force and can be used on declarations of conformity (DOCs).

*_REPEAL_*
Similarly, both directives state the older directives (2004/108/EC and 2006/95/EC) are "repealed with effect from 20 April 2016, without prejudice to the obligations of the Member States relating to the time limits for transposition into national law and the dates of application set out" in the new directives (2014/30/EU and 2014/35/EU). As a result, any products that still relies on the old directives for CE compliance may not be imported and sold after 20 April 2016.

Fortunately, both new directives do state that any "references to the repealed Directive shall be construed as references to this [new] Directive and shall be read in accordance with the correlation table given" in the new Directive. As a result, as long as the product still complies with the new directive and just has documentation making outdated references to the old directive.

So ... if you are correct that EU directives are "aren't valid until ALL member states have implemented them", I would like to know the official document that contradicts the EU directives themselves.

Thanks.
Monrad


On 3/2/2015 12:50 PM, John Woodgate wrote:

    In message <[email protected]>
    <mailto:[email protected]>, dated Mon, 2
    Mar 2015, "Ron Pickard (RPQ)" <[email protected]>
    <mailto:[email protected]> writes:


    As I believe as Mr. Woodgate pointed out earlier, these new
    directives have no legal standing until at least one member state
    enacts them into their own legal system. To my knowledge, that
    hasn't happened yet. Anyone have any info on this?


    There has been a new ruling on this from the Commission. One
    implementation is NOT ENOUGH: the Directives aren't valid until
    ALL member states have implemented them.

    I suppose this is because a member state could find a serious
    objection to implementation, which would put everything back in
    the melting pot.



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to