Reference articles 250 and 690 of the NEC (NFPA70). Canada and Mexico code 
similar.

Brian

From: Boštjan Glavič [mailto:bostjan.gla...@siq.si] 
Sent: Monday, February 15, 2016 9:05 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] grounding of output of solar inverter

Dear experts,

Is anyone familiar with UL 1741? I am dealing with solar inverter for US 
market. Solar inverter can operate in utility interactive mode (feeding the 
grid) or in  a standalone mode where only homeloads are supplied by inverter 
(anti-islanding relays are open, due to problems with the grid). When 
anti-islanding relays are open, I have an issue of grounding the neutral 
conductor of output for homeloads. How can this grounding be achieved? Clause 
19.2 does not allow grounding inside the unit (or I have  understood it 
incorrectly and it only prohibits fixed connection) and clause 19.3 requires 
that output is grounded. Below is extract from the standard.
Any idea? I think it is the same issue as with UPS.

19.2 An inverter intended to be utility-interactive shall not have a 
direct/solid electrical connection between any output ac conductor and the 
enclosure.

19.3 Other than as specified in 19.2, each ac output circuit shall have a 
grounded conductor. The ac output circuit conductor to be grounded shall be as 
follows:
a) Single-phase, 2-wire - one conductor.
b) Single-phase, 3-wire - the neutral conductor.
c) Multiphase system having one wire common to all phases - the common 
conductor.
d) Multiphase system in which one phase is used as in item (b) - the neutral 
conductor.

19.4 The conductor specified in 19.3 is to be connected by a bonding jumper 
connected between the grounded conductor and:
a) The enclosure of a metal-enclosed unit, or
b) For a nonmetallic enclosed unit, the metal chassis that is bonded to the 
equipment grounding
conductor or terminal. See 18.2.1.

Thank you for your support.

Best regards,
Bostjan

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to