Dear Ken, Brian,

Thank you for your reply. I know requirement of CSA No. 04 and all shelfs are 
compliant to this requirement since US/CAN ND required short-trace test. 
However new standard has a bit different requirement and I would like to find 
rationale for 25A protective current rating. Why this solution is not 
acceptable any more.

I really need to be sure before I made a non-compliant report to the customer.

Best regards,
Bostjan



> On 27. jun. 2016, at 18.36, Brian O'Connell <oconne...@tamuracorp.com> wrote:
> 
> And an additional note that the CSA No. 0.4 test done at 40A.
> 
> Brian
> 
> 
> From: IBM Ken [mailto:ibm...@gmail.com] 
> Sent: Monday, June 27, 2016 8:33 AM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: Re: [PSES] earthing through PCB traces
> 
> PS: UL/CSA 60950 always required a limited short circuit test from CSA C22.2 
> No. 0.4 for "protective bonding conductors and their terminals of 
> non-standard constructions, such as printed wiring protective traces" as a D1 
> deviation, so if these products were sold in North America they should 
> already be compliant somehow. 
> 
> -Ken
> 
> On Mon, Jun 27, 2016 at 11:09 AM, IBM Ken <ibm...@gmail.com> wrote:
> Hi Bostjan!
> It looks like 5.6.4.1 gives you four choices:
> 
> (1) Minimum conductor sizes in G.5
> 
> or (if, presumably, you don't meet the minimum conductor sizes in G.5)
> 
> (2) Meet 5.6.6 (test).  If (and only if) the protective current rating is 
> >25A you also have to meet Table 31 (in general, the requirements of Table 31 
> are easier to meet than Table G.5.)
> My assumption is that if the protective current rating is <=25A you do not 
> have to meet Table 31 but you still have to meet the test of 5.6.6
> 
> Or (if, again, you don't meet the minimum conductor sizes in G.5)
> 
> (3) Meet 5.6.6 (Test).  If the protective current rating is <=25A you can 
> either  meet table 31 - or - Perform limited short circuit test from Annex R
> 
> (4) For components only, protective bonding conductors must be not smaller 
> than the supply conductors
> 
> My interpretation would be that if you have equipment with protective 
> conductor rating >25A which can't meet (4) or (1), you have to pass the 5.6.6 
> test and the conductors must also meet Table 31.  Therefore, it seems that 
> constructions with protective current rating >25A are prohibited from using 
> PCB traces for bonding.   On the other hand, Table 31 just says "Minimum 
> protective bonding conductor size of copper conductors".  What if the PCB 
> trace cross-sectional area is greater than or equal to the cross-sectional 
> area stated in table 31?  Meeting Table 31 on PCB traces would result in very 
> wide traces but it doesn't seem to be prohibited the way 62368 is worded.
> 
> -Ken
> 
> 
> On Mon, Jun 27, 2016 at 9:03 AM, Boštjan Glavič <bostjan.gla...@siq.si> wrote:
> Dear Experts,
>  
> I need your opinion about requirements of IEC 62368-1 standard. Standard 
> requires special limited short-circuit test on earthed accessible parts that 
> are earthed through PCB traces. However this test is only applicable if 
> protective current rating is below 25A according to clause 5.6.4.1.
>  
> What about the products with protective current rating above 25A? Standard 
> does not say that such constructions are not allowed, just does not specify 
> requirements.
>  
> Many telecom power shelfs, composed of hot-pluggable power supplies and 
> backplane are using PCB traces for earthing of the power supply enclosure. It 
> is normal to have protective current rating above 25A in this case. How to 
> deal with this situation? All power supply shelfs already have IEC 60950-1 
> certificate.
>  
> Thank you for your opinion.
>  
> Best regards,
> Bostjan Glavic
> SIQ
> 
> -
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society emc-pstc 
> discussion list. To post a message to the list, send your e-mail to 
> <emc-p...@ieee.org>
> 
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
> 
> Attachments are not permitted but the IEEE PSES Online Communities site at 
> http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
> formats), large files, etc.
> 
> Website:  http://www.ieee-pses.org/
> Instructions:  http://www.ieee-pses.org/list.html (including how to 
> unsubscribe)
> List rules: http://www.ieee-pses.org/listrules.html
> 
> For help, send mail to the list administrators:
> Scott Douglas <sdoug...@ieee.org>
> Mike Cantwell <mcantw...@ieee.org>
> 
> For policy questions, send mail to:
> Jim Bacher:  <j.bac...@ieee.org>
> David Heald: <dhe...@gmail.com>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to