Thank you Ted. That was actually a concern of the customer if there is an 
arcing. Or for example if unit is broken(damaged basic insulation to PE) and 
plugged into the rack. Can it result in hazardous situation?

One thing also bothers me. In hazard based standard there is no requirement for 
distance between tip of the test finger and bare hazardous part if voltage is 
below 420V.  The air will not break down because of Paschens law.

So can I expect the same for module that is plugged into the rack - no arcing?

Best regards
Bostjan





On 2. dec. 2016, at 22.42, Ted Eckert 
<000007cf6ebeab9d-dmarc-requ...@ieee.org<mailto:000007cf6ebeab9d-dmarc-requ...@ieee.org>>
 wrote:

I would also recommend considering the anticipated voltages on the connector. 
Higher voltages are capable of arcing across larger air gaps, and they would 
require keeping the ground engaged past the point where the air gap is large 
enough to suppress arcing.

Ted Eckert
Microsoft Corporation

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: Richard Nute [mailto:ri...@ieee.org]
Sent: Friday, December 2, 2016 10:10 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] pre-mating of PE in hot-plug connector


The requirement is, as you have quoted, that the PE connection mate first and 
break last.  There is no dimensional requirement as such will be a function of 
the overall design.

The requirement must be met when mating planes are not parallel due to the 
design and tolerances of the parts.

Rich



From: Boštjan Glavič [mailto:bostjan.gla...@siq.si]
Sent: Friday, December 02, 2016 3:45 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: [PSES] pre-mating of PE in hot-plug connector

Dear Experts,

One customer is designing own connector for hot-plug application (power 
supply). Question is how much longer shall be PE pin than supply pins. Which 
standard shall be used for such connector?

For reference you can see similar connector on below link.

http://www.harting.com/en/service/catalogues/downloads-and-order-connectivity-networks/din-41612-connectors/


I have checked UL 1977 and there is no such requirement.

Somewhere I found a note that applicable standard is IEC 60603-2 however I am 
not sure if requirement for dimension of PE pin is included.

I am surprised that no such requirement exist in IEC 60950-1 or IEC 62368-1. 
They just mention in clause 2.6.5.4 that PE connection shall make earlier and 
brake later than the supply connections.

Any idea?

Thank you for your support.

Best regards,
Bostjan


-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to