Standards committees will re-use text if no-one tells them not to. It may take 
many tellings, too.  It took me several years to get a total nonsense statement 
about diodes deleted from IEC 60384 and  equally long times to get a typo in 
the electrochemical table in IEC 60065,60950-1 and 62384-1 fixed. But the 
longest time was taken in getting the specification of 'petroleum spirit' 
changed from a misinterpretation to a realistic statement.
 
With best wishes DESIGN IT IN! OOO – Own Opinions Only
 <http://www.jmwa.demon.co.uk/> www.jmwa.demon.co.uk J M Woodgate and 
Associates Rayleigh England
 
Sylvae in aeternum manent.
 
From: Doug Powell [mailto:doug...@gmail.com] 
Sent: Friday, January 6, 2017 2:32 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Thermal equilibrium - 10% rule
 
I agree that thermal equilibrium can never be achieved especially in light of 
the zeroth law of thermodynamics, but also for more reasons than the 
exponential nature of the thing.  Possibly a better phrase to use is thermal 
stability.  
 
I actually believe that the standards committees will re-use the text of 
previous standards and averse to changing it in subsequent revisions with the 
rationale that it worked in the past and possibly there's someone relying on 
this bit of information.  The 10 percent of the previously elapsed time 
business simply does not make sense to me and I have never used it in actual 
testing.  Nevertheless, it has shown up in a couple of recently published 
standards I use for large format storage batteries.
 
In my case, I have an outdoor product that weighs in at more than 100,000 
pounds and thermal equilibrium cannot be achieved in 24 hours, meanwhile the 
daily cyclical temperature compound the problem of measurement.  Obviously, I 
am going to have to do live compensation of ambient conditions during the test 
and not afterward.  
 
Thanks all,
 
Doug
 
 
 
 
On Fri, Jan 6, 2017 at 12:31 AM, John Woodgate <jmw1...@btinternet.com 
<mailto:jmw1...@btinternet.com> > wrote:
Only that , even with cooling and conductor resistivity taken into account, the 
approach to equilibrium is still very nearly exponential (the resistivity 
change is non-linear) , so in theory takes infinite time.
 
With best wishes DESIGN IT IN! OOO – Own Opinions Only
 <http://www.jmwa.demon.co.uk/> www.jmwa.demon.co.uk J M Woodgate and 
Associates Rayleigh England
 
Sylvae in aeternum manent.
 
From: Ken Javor [mailto:ken.ja...@emccompliance.com 
<mailto:ken.ja...@emccompliance.com> ] 
Sent: Friday, January 6, 2017 3:18 AM

To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Subject: Re: [PSES] Thermal equilibrium - 10% rule
 
Understand I’m not arguing with Rich Nute on a topic with which I have little 
familiarity. I’m just looking at the physics of heat transfer. If I am running 
current through a conductor that causes its temperature to rise, then as 
temperature rises, according to Newton’s Law of Cooling, more heat is 
transferred from the hot body to the cooler surroundings, in direct proportion. 
 So at some point the temperature will equilibrate because the heat energy 
radiated/convected/conducted to the surroundings will equal the electrical 
energy dissipated in the conductor.

What am I missing? 

Ken Javor
Phone: (256) 650-5261 <tel:(256)%20650-5261> 

  _____  

From: Richard Nute <ri...@ieee.org <mailto:ri...@ieee.org> >
Reply-To: <ri...@ieee.org <mailto:ri...@ieee.org> >
Date: Thu, 5 Jan 2017 17:03:36 -0800
To: <EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> >
Subject: Re: [PSES] Thermal equilibrium - 10% rule

 
Thermal equilibrium is impossible.  Thermal change is an exponential, never 
achieving the end-point.  
 
The test is to determine that some part does not exceed its temperature rating. 
 Plotting the (exponential) curve shows whether the temperature in question is 
or is not going to exceed its rating.  (Curve-fitting would be nice, but 
impossible.)  As soon as this determination is made, the test can be concluded.
 
Defining thermal equilibrium as ±2°C (3.6°F) is not achievable as thermal 
change is an exponential.  And, it is tight.  For a small (low thermal mass) 
part, air currents will change the temperature beyond this limit.
 
The statement does not reflect knowledge of primitive thermodynamics.  
 
Best wishes for the New Year!
Rich
 
 

From: Doug Powell [mailto:doug...@gmail.com] 
Sent: Thursday, January 05, 2017 2:47 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Subject: [PSES] Thermal equilibrium - 10% rule


All,

 

The following has always been confusing for me, 

 

For those tests that require the DUT to reach thermal equilibrium, thermal 
equilibrium is considered to be achieved if after three consecutive temperature 
measurements taken at intervals of 10% of the previously elapsed duration of 
the test but not less than 15 min, indicate no change in temperature greater 
than ±2°C (3.6°F).

 

The portion of text "taken at intervals of 10% of the previously elapsed 
duration of the test" has been around for some time and it exists in several 
safety standards, the "not less than 15 min" can be other values like 10 
minutes, 5 minutes, etc.  I believe the intent is to minimize the number of 
data points being recorded for extremely long thermal tests. The idea makes 
sense when I think back to the days of manual data logging.  Nowadays, with the 
advent of automated data logging, this point probably becomes moot.  Still, the 
phrase bugs me and I would like to understand how this might be interpreted.

 

First the "previously elapsed duration" could indicate either the duration of 
the entire test or the duration of the last logging interval.  

 

Second, over a long test 10% of the previous interval very quickly shortens the 
logging intervals to something ridiculously small.  For example, in three data 
points interval of 1440 minutes (24 hours) will be reduced to 144 minutes (2.4 
hours) and then 14.4 minutes, at which point the 15 minute minimum takes over.

 

I generally record at a much shorter intervals, even if for several days and 
check for equilibrium at a modulus of 15 minutes, as required.

 

 

 

​Thanks,  Doug

​
 
-- 

 
Douglas E Powell

doug...@gmail.com <mailto:doug...@gmail.com> 
http://www.linkedin.com/in/dougp01
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:      http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe)  <http://www.ieee-pses.org/list.html> 
<http://www.ieee-pses.org/list.html> 
List rules:     http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org> >
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> > 

For policy questions, send mail to:
Jim Bacher  <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> > 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org> >
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> > 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> > 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
&LT;emc-p...@ieee.org <mailto:emc-p...@ieee.org> &GT;
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas &LT;sdoug...@ieee.org <mailto:sdoug...@ieee.org> &GT;
Mike Cantwell &LT;mcantw...@ieee.org <mailto:mcantw...@ieee.org> &GT; 
For policy questions, send mail to:
Jim Bacher &LT;j.bac...@ieee.org <mailto:j.bac...@ieee.org> &GT;
David Heald &LT;dhe...@gmail.com <mailto:dhe...@gmail.com> &GT; 



 
-- 
 
Douglas E Powell

doug...@gmail.com <mailto:doug...@gmail.com> 
http://www.linkedin.com/in/dougp01
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org> >
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> > 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> > 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to