Yes, the marking on these is not well-formatted. The three numbers are
*independent* limits, the 3680 W being 16 A at 230 V, but the strip could be
used on supplies up to 250 V as long as neither of the other limits was
exceeded.
 
Better would be 'Maximum ratings: 16 A, 250 V, 3680 W'
 
With best wishes DESIGN IT IN! OOO - Own Opinions Only
 <http://www.jmwa.demon.co.uk/> www.jmwa.demon.co.uk J M Woodgate and
Associates Rayleigh England
 
UK is a sovereignty, not a Zollverein-ty
 
From: Don Gies [mailto:ddg...@verizon.net] 
Sent: Friday, September 15, 2017 1:16 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
 
Pete,
 
Before last year's TC108 meeting in Frankfurt, I purchased a German Schucko
European Power Strip from Amazon.  It had 3 AC receptacles and 2 USB
outputs. 
 Its ratings are:
"Maximum Charge: 3680W,16A/250V~    "
 
Don Gies
 <mailto:ddg...@verizon.net> ddg...@verizon.net
(732) 207-7828
 
From: John Allen [mailto:000009cc677f395b-dmarc-requ...@ieee.org] 
Sent: Friday, September 15, 2017 4:32 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Subject: Re: [PSES] power strip details
 
Unlike the US/Canada (etc), there is no derating factor for UK mains wall
outlets. A 13A wall outlet can be loaded at 13A, and a twin/duplex 13A
outlet can be loaded at 13A per outlet because the "diversity factor"
principle is applied, i.e. it is highly unlikely in practice that both 13A
outlets will be actually be fully loaded at the same time! 
 
Murphy's Law may however apply at times in that both outlets could
simultaneously be loaded at 13A - and so it is to be hoped that the wall
outlet in question is on a UK "ring main" circuit protected by a 32A
breaker, and not a spur/radial/branch circuit protected by a 16A breaker!
 
For a power strip plugged into one of those outlets, there is a (generally,
as John W said) a 13A fuse in the plug, and so the max cumulative continuous
load for the sockets in the strip is also 13A - unless, of course, the mfr
has decided to give it an overall lower current rating, fitted a lower-rated
fuse AND marked the plug with that rating. BTW: I have also occasionally
seen 7A fuses (the fuse standard is BS1362, but, AFAIK, that only shows a
few "standard" ratings, and not some of those which are actually sold - such
as those listed here http://cpc.farnell.com/search?st=plug%20top%20fuse)
 
I believe that the standard for such UK power strips is probably BS
5733:2010+A1:2014 "General requirements for electrical accessories.
Specification" - but don't have a copy and so can't comment in detail on
what it requires.
 
John Allen
W.London, UK
 
 
 
From: John Woodgate [mailto:jmw1...@btinternet.com] 
Sent: 15 September 2017 07:36
To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Subject: Re: [PSES] power strip details
 
UK household power strips are rated at 13 A and include a 13 A fuse. Other
fuses, normally used in plugs, are 3 A, 5 A and 10 A. I have seen a 1 A
fuse, but they are very rare.
 
With best wishes DESIGN IT IN! OOO - Own Opinions Only
www.jmwa.demon.co.uk <http://www.jmwa.demon.co.uk/>  J M Woodgate and
Associates Rayleigh England
 
UK is a sovereignty, not a Zollverein-ty
 
From: Pete Perkins [mailto:00000061f3f32d0c-dmarc-requ...@ieee.org] 
Sent: Friday, September 15, 2017 5:55 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Subject: [PSES] power strip details
 
Esteemed colleagues,
 
                Here in North America a domestic or commercial multi-outlet
power strip would be cord connected thru a duplex outlet protected by a 15A
(or sometimes 20A) circuit breaker.  The max load allowed in the circuit by
the US NEC would be (80% of 15A) 12A for the total load (or 80% of 20A) 16A
on the 20A breaker.   Note that the US NEC requires that any device plugged
into a duplex outlet must not use the full load capacity of the circuit -
20% must be left for the other outlet's load.  
 
                Trying to understand the loading basis for a Euro power
strip.  Is the usual protection a 10A breaker? And would the power strip be
rated and evaluated at that load level?  What other considerations come into
play here?  
 
                How about a UK power strip.   The usual protection is the
13A fuse in the power plug (altho smaller values seemed to be used also).
Would the power strip be rated and evaluated at that load level?  What other
considerations come into play here.  
 
                For a Japanese power strip what is the normal breaker
protection for the installed circuit?  What would be the max rated load for
the power strip?  What other considerations come into play here also?  
 
                Looking forward to your replies on this issue.  
 
:>)     br,      Pete
 
Peter E Perkins, PE
Principal Product Safety & Regulatory Affairs Consultant
PO Box 23427
Tigard, ORe  97281-3427
 
503/452-1201
 
p.perk...@ieee.org <mailto:p.perk...@ieee.org> 
 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org> >
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> > 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> > 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org> >
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> > 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> > 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org> >
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> > 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> > 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org> >
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> > 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> > 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to