Hello Brian,

This falls under the issue of “continuous” vs. “non-continuous” loads. NFPA 70, 
section 210.19 is one of the clauses that sets the requirement for the 80% 
derating. However, it states: “Where a branch circuit supplies continuous loads 
or any combination of continuous and noncontinuous loads, the minimum 
branch-circuit conductor size shall have an allowable ampacity not less than 
the noncontinuous load plus 125 percent of the continuous load.”

“Continuous” is a load intended to be used for 3 hours or more. A hairdryer or 
microwave are not “continuous”. (If they are, you either have too many dogs and 
need to stop walking them in the rain or you like cooking food until it tastes 
like charcoal.)

The problem is that a detachable cord with an appliance coupler could be used 
with any product. Unless it has a built-in timer, you have no way of 
guaranteeing that it won’t be used with a product that draws current for less 
than 3 hours. There may be “non-continuous” loads with an appliance coupler and 
rated for 15 A. As such, I would expect such a detachable cord to need to be 
rated for at least 15 A.

A cord with a NEMA 5-20P would then be prohibited from having a C13 connector 
at the other end. It would need a C19 instead.

That being said, for some specialty industries, you can find some strange 
combinations of plugs and receptacles.
http://www.marinco.com/en/s15-504

Ted Eckert
Microsoft Corporation

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Monday, October 9, 2017 8:31 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] NEMA 5-20P with IEC 60320 C13

It is my understanding that according to the US National Electric Code, 15 amp 
receptacle are derated to 12 amps max., and 20 amp receptacles are derated to 
16 amps.

IEC 60320 C13 connectors are rated 15 amps in North America. Do I derate them 
as well or can I draw 15 amps continuous from the C13 connector?

So here is the big question:

If I have a power cord with a NEMA-5-20P at one end, IEC 60320 C13 at the other 
end, and 14awg cordage (rated 18A), can I use/ship this power cord with a 
product rated 15 amps?

Thanks to all.
The Other Brian
________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=KPn0zexfjGkIaute9FWGP4vvV00uCRcuq6GtjQwrsoc%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=q%2FDeWz1bT6EE9ZzNJ6pCeXkgJ15OalJ9h%2FLcaw3NxwE%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=cqdYdOYIlOCxox3pWdNSzaHQ8h78bRZpog6wz48PYUU%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=pTffGjqXHDDcluuvgpr4zQcuPEaUev8Wfdu%2BM13esH0%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=zlByB75xMImmpqiaNEUPl6kS0%2Bqf%2B%2BcdBD%2BQqP6OjDs%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to