Thank you Dave and John for your answers.

The question is if the equipment is a control panel made of off-the-shelf 
components with UL/CE mark,
1. then UL 508A should be enough or do we need to apply UL 61010-1 or NFPA79?
2. In the case of Europe, EN 60204-1 should be enough then?

Thank you for your answers

Kind Regards / Saludos cordiales / Mit freundlichen Grüßen
Daniel Rodríguez

From: Nyffenegger, Dave <dave.nyffeneg...@bhemail.com>
Sent: Friday, 13 December 2019 14:07
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] UL508A vs UL61010-1 for control and monitoring equipment

Caution: This email originated from outside of the organization. DO NOT CLICK 
on links or open attachments unless you recognize the sender and know the 
content is safe.


UL 508A is intended to cover the control panel itself while 61010-1 applies to 
the "equipment" it is used in.    That being said I have had NRTLs apply 508A 
to machinery "equipment" using such control panels (not separately listed) 
because they have to use "some" UL standard for an NRTL listing, and use NFPA 
79 for the equipment standard.  NFPA 79 is harmonized with EN 60204-1.
-Dave

From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Friday, December 13, 2019 4:01 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] UL508A vs UL61010-1 for control and monitoring equipment


Hello, Daniel. The word is actually 'criterion', 'criteria' is plural.

UL508A seems to be restricted to something that switches other things on or 
off, or alters their operating modes.  UL61010-1 is for something that sends 
analog or digital control values, such as heater temperature or rate of 
rotation, to other things. If your panel does that, 61010-1 applies.

Best wishes and seasonal felicitations

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates 
www.woodjohn.uk<https://urldefense.com/v3/__http:/www.woodjohn.uk__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMhL1t2kx$>

Rayleigh, Essex UK
On 2019-12-13 08:50, Rodriguez, Daniel (ESP) wrote:
Good morning    all
I have a industrial control equipment with sensors and flowmeters made in an 
electrical panel of standard components.
Is there a criteria to use UL508A or UL61010-1?

It seems that UL508A is applicable for:
This equipment consists of assemblies of two or more power circuit components, 
such as motor
controllers, overload relays, fused disconnect switches, and circuit breakers, 
or control circuit
components, such as pushbuttons, pilot lights, selector switches, timers, and 
control relays, or a
combination of power and control circuit components, with associated wiring, 
and terminals . These
components are mounted on, or contained within, an enclosure, or are mounted on 
a sub-panel.

And UL61010-1 is for
Electrical industrial process-control equipment
This is equipment which controls one or more output quantities to specific 
values, with
each value determined by manual setting, by local or remote programming, or by 
one or
more input variables.

But it is not clear if a industrial panel made of UL approved components needs 
to be certified for UL508A or can be UL61010-1? Or there is any restriction

Thank you for your answer

Kind Regards / Saludos cordiales / Mit freundlichen Grüßen
Daniel Rodríguez

CONFIDENTIALITY NOTICE: This e-mail communication and any attachments may 
contain proprietary and privileged information for the use of the designated 
recipients named above. Any unauthorized review, use, disclosure or 
distribution is prohibited. If you are not the intended recipient, please 
contact the sender by reply e-mail and destroy all copies of the original 
message.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://urldefense.com/v3/__http:/www.ieee-pses.org/emc-pstc.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMs3qk9Pp$>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://urldefense.com/v3/__http:/product-compliance.oc.ieee.org/__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMjjbXXBa$>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://urldefense.com/v3/__http:/www.ieee-pses.org/__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMpwjLGgt$>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__http:/www.ieee-pses.org/list.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMnD94uXV$>
List rules: 
http://www.ieee-pses.org/listrules.html<https://urldefense.com/v3/__http:/www.ieee-pses.org/listrules.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMrUj5t7s$>

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://urldefense.com/v3/__http:/www.ieee-pses.org/emc-pstc.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMs3qk9Pp$>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://urldefense.com/v3/__http:/product-compliance.oc.ieee.org/__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMjjbXXBa$>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://urldefense.com/v3/__http:/www.ieee-pses.org/__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMpwjLGgt$>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__http:/www.ieee-pses.org/list.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMnD94uXV$>
List rules: 
http://www.ieee-pses.org/listrules.html<https://urldefense.com/v3/__http:/www.ieee-pses.org/listrules.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMrUj5t7s$>

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://urldefense.com/v3/__http:/www.ieee-pses.org/emc-pstc.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMs3qk9Pp$>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://urldefense.com/v3/__http:/product-compliance.oc.ieee.org/__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMjjbXXBa$>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://urldefense.com/v3/__http:/www.ieee-pses.org/__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMpwjLGgt$>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__http:/www.ieee-pses.org/list.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMnD94uXV$>
List rules: 
http://www.ieee-pses.org/listrules.html<https://urldefense.com/v3/__http:/www.ieee-pses.org/listrules.html__;!!Nkc5UzxO!_-fx1OgqIDOzUnivvMN-RT9k91ib0I4UqdYCq9FJVy7XKZK4LSG-TqwfMrUj5t7s$>

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to