The NEC 670.6 quote triggers some questions:

 

I wonder why industrial machinery with a safety interlock is required to have 
surge protection as opposed to machinery that does not have an interlock?

 

Is an “on-off” or “run-stop” control considered a “safety interlock”?

 

Is the “surge” a higher-than-normal power-line voltage or is it an impulse from 
switching or lightning?

 

Does “effectively protected” mean passing the dielectric (hi-pot) test?

 

Richard Nute

Bend, Oregon, USA

(Several inches accumulation of snow this morning, but above freezing.)

 

 

From: Doug Powell <doug...@gmail.com> 
Sent: Tuesday, November 1, 2022 11:28 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Surge Protection Device required by NEC

 

>From the 2020 Edition, emphasis is mine.

 

"670.6 Surge Protection. Industrial machinery with safety interlock control 
devices not effectively protected from voltage surges on the incoming supply 
circuit shall have surge protection installed."

 

It does not say where this protection needs to be applied, so I assume it can 
be within the machine or somewhere in machine supply. Also, does the product 
you are inquiring about fall under the definition of Industrial Machinery, NFPA 
79? 

 

-Doug

 

Douglas E Powell

Laporte, Colorado USA

 <mailto:doug...@gmail.com> doug...@gmail.com

 <https://www.linkedin.com/in/coloradocomplianceguy/> LinkedIn

 

(UTC -06:00) Mountain Time (US-MDT)

 

 

 

On Tue, Nov 1, 2022 at 11:55 AM Brian Kunde <bkundew...@gmail.com 
<mailto:bkundew...@gmail.com> > wrote:

It just came to my attention that section 670.6 of the US National Electric 
Code 2017 requires a listed Surge Protection Device (SPD) to be on any 
Industrial Machine that has an Interlock, or I assume any kind of safety 
function.  Is this true? The only information I can find on the internet is 
from the companies that make and sell the SPDs which can often be very one 
sided.  Is there more to this story that I am missing?

 

Does the Surge Protection have to be listed? Are there specifications for the 
SPD? Is there a Surge Immunity Test that be used to validate and verify whether 
an additional SPD is required or not?  

 

Thanks,

The Other Brian


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to