Jon Elson wrote:

>>For speed:
>>The max jog speed is set in emc to 90 ipm (1.5 in/sec). When jogging at 
>>the max rate I measured a step frequency of 813 Hz on phase A.
>>Calculating the table speed:
>>800 pulses/sec x 60 sec/min x .0004 in/step = 19.2 ipm
>>However just by looking at the table move, it is moving much faster than 
>>that.
>>Is this because due to the nature of quadrature drive, the table 
>>actually moves 4 times faster than the step rate?
>>    
>>
>Yes, precisely.  Every change of either A or B is a "full step" 
>of the motor.  813 Hz should give 3252 steps/second, or 78 IPM.
>I'm not sure why you aren't getting the full 90 IPM you are 
>requesting.
>
>  
>
Well it's probably because of my halscope measurement. 
When using the fast thread for a halscope trigger, it retriggers when 
the buffer fills. Consequently when you stop the jog it begins 
decelerating and the buffer can fill and cause a retrigger during this 
phase.  I tried to get around this problem by hitting "machine off" as  
I stopped jogging.  So the reading I got in halscope I'm sure was 
probably during the beginning of the deceleration period. 

Using a real analog scope I measured about 1 Khz.  This calculates to 96 
ipm.  So at 90 ipm my scope reading should have indicated a period of 
1.06 millisec => 938 Hz.  This is within the accuracy of my reading the 
scope and its error.

Jack Ensor

-------------------------------------------------------------------------
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to