> > I would also think there is some issue with ground (broken wire?) or
> > with configuration (assuming hardware is OK of course) -- I got the
> > same VFD in my Biesses, and although they seem a bit noisy
> > (touchscreens nearby doen't work as soon as spindle starts despite
> > shielded motor cables and proper grounding), vfd and motor work ok.
> > analog signals are coming from 7i48, connected to pins 4 and 5.
> > start/stop signals etc... is driven by original wiring and relay break
> > out boards.
> > 
> 
> Thank you Gene and others for the tips! I did fix it but am not sure
> what was the cause - with wires removed from VFD the analog output was
> stable. Connecting cables to VFD and it was fluctuating. In the end it
> was stable if I removed the wires from VFD to 7i37 board that provide
> "run" and "stop" signals for VFD. I just introduced 2 relays inbetween
> and now it kinda works.

A VFD is usually a very good noise generator so should come as no surprise.


> Robert I was hoping that your experience might help on this as I am
> getting something that I have not seen before - with pwmgen value = 0
> there are 0.3V on the actual analog output (that is approximately 1/30
> of the full range so should give about 10Hz on VFD output as I have
> 0-300Hz range specified in Pr0 and Pr1) but the VFD runs the motor at
> much higher speed - the frequency matches Prc parameter in VFD.

Voltage drop on ground signal?

...

Nicklas Karlsson



_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to