Hi Ulf, There is an issue with the S series drives. Firstly, they pronounce they are ready before they really are. This can cause problems in the master when it tries to get the slave PDO config. It will revert to what is in the e2 memory which isn't always the same as the device. You should remove the PDO config from the e2, or wait for the drive to fully come up before starting the master.
Secondly, the drive defaults to synchronous mode! This needs you to set up DC's, define the access frequency and keep to it! There is a magic SDO to put it into asynchronous mode ie ecrt_slave_config_sdo32(sc,0x3691,1,0x20000); regards Ian -----Original Message----- From: [email protected] [mailto:[email protected]]on Behalf Of Ulf Stelbe Sent: 21 April 2010 13:40 To: [email protected] Subject: [etherlab-users] Slave state changing from SAFEOP to OP Hello, I use the user sample to get a S700 servo drive running. Initialization is done well and the cyclic task is performed. But the slave keeps in SAFEOP state. What to do to get it into OP? The servo manual states: The amplifier goes into OP after succesful sync and the sync warning n17 (I get this warning) is cleared. If not, the sync error F28 is set (I get this after a short time). What do I do wrong? The slave should go into OP automatically after sync with the master, right? Any help is appreciated! Thanks in advance Ulf Stelbe ______________________________________________ OTLO VR Systeme GmbH Zelckstraße 13, 18055 Rostock Email: [email protected] Web : www.otlo.de Tel. : +49 381 44 03 59 30 Fax. : +49 381 44 44 232 Amtsgericht Rostock, HRB 8874 GF: Ulf Stelbe, Dr.-Ing. Nico Günther _______________________________________________ etherlab-users mailing list [email protected] http://lists.etherlab.org/mailman/listinfo/etherlab-users _______________________________________________ etherlab-users mailing list [email protected] http://lists.etherlab.org/mailman/listinfo/etherlab-users