I'm not familiar with that specific slave, but if a slave has reconfigurable 
PDOs then you may be required to actually configure them before you can 
successfully communicate with it.

This requires calling ecrt_slave_config_pdos with the appropriate PDO 
definitions, which must be compatible with some configuration that the slave 
supports (check the syslog when you activate the master to see if there are any 
errors occurring during configuration, possibly with "ethercat debug 1" active 
before running your app).  See the example code included with Etherlab.

(If you don't call this, then Etherlab assumes the slave's default PDO layout, 
which might be empty for some slaves.  If you do call it with invalid 
arguments, then depending on the slave it may be left with its original 
configuration, an empty configuration, or some subset of your intended 
configuration.)

Some slaves may also require specific SDO setup before entering OP state - you 
can use ecrt_slave_config_sdo* functions to register these.  (Note that you 
should not use this to configure the PDO Config/Assign objects; that's what the 
previous function takes care of for you.)

The slave device's manual should explain the supported PDO layouts and other 
configuration options.


Gavin Lambert
Senior Software Developer

[cid:logo_compac_5dcf97ef-52f5-498c-8b9b-728410ddffaf.png]
[cid:compacicon_82e8a8c7-154a-4a32-9720-a5badb6258e0.png]<http://www.compacsort.com>
 [cid:facebook_fa85b924-53b9-45cc-8162-0564f64ec3a3.png] 
<https://www.facebook.com/Compacsort>  
[cid:linkedin_4ec016ad-84fa-443c-85a3-b9615a4ccef8.png] 
<https://www.linkedin.com/company/compac-sorting-equipment/>  
[cid:youtube_32142163-fc27-4aed-b14d-e8a377f98a6d.png] 
<https://vimeo.com/compacsort>  
[cid:twitter_d89338d8-98c8-4b65-9a9e-7b1333160b0d.png] 
<https://twitter.com/compacsort>

COMPAC SORTING EQUIPMENT LTD | 4 Henderson Pl | Onehunga | Auckland 1061 | New 
Zealand
Switchboard: +64 96 34 00 88 | tomra.com<http://www.tomra.com>

The information contained in this communication and any attachment is 
confidential and may be legally privileged. It should only be read by the 
person(s) to whom it is addressed. If you have received this communication in 
error, please notify the sender and delete the communication.

From: etherlab-users <[email protected]> On Behalf Of 
Matthias Bartsch
Sent: Monday, 18 February 2019 23:47
To: '[email protected]' <[email protected]>
Subject: [etherlab-users] EtherCAT slave B&R X20 IF 10G3 goes into operatonal 
mode but doesn't update the process image

Hello @all!

I'm trying to use a "B&R X20 IF 10G3" EtherCAT  interface device with the IgH 
1.5.2 EtherCAT master and Gavin's patch set 20171102.
The B&R device use the Hilscher EtherCAT slave implementation.
The configuration and startup  of the device seems OK and the device is going 
into operational state. But the working counter for the device isn't increased 
and no cyclic (PDO) communication is possible.
Access via SDO in preoperational state works.
I have checked the communication with TwinCAT and it's working. TwinCAT doesn't 
set any special SDO at startup and the addresses of the sync managers seems to 
be the same as the IgH stack uses.
I have also created a new SII eeprom image from the slaves ESI file but no 
success.
Has somebody faced already a similar situation?
I have logged the startup sequence with wireshark and itlooks like that TwinCAT 
configures every parameter each time  when it starts but the IgH stack doesn't 
do that (maybe because the settings from the SII memory are the same used for 
the communication?). I'm not so familiar in interpreting the wireshark log so 
maybe somebody can give me an advice what's maybe the problem.

Best regards