The regulation is 1 gallon per every 24 square feet of laboratory.
René J.

--- On Wed, 1/20/10, Green JumpyOne <greenjumpy...@hotmail.com> wrote:


From: Green JumpyOne <greenjumpy...@hotmail.com>
Subject: [Histonet] flammable liquid storage
To: histonet@lists.utsouthwestern.edu
Date: Wednesday, January 20, 2010, 11:14 AM



I was told that we are allowed to have 2 gallons of flammable liquid contained 
within a flammable cabinet per 100 sq. ft.  My question is the following:  Is 
that square footage for the *entire* clinical laboratory or *only* the 
histology area of the lab?  My inclination is to say the entire clinical lab, 
not just histo, but I need to be certain.

I am referring to the AHCA NFPA 99 item 11.7.2 for the state of Florida.  The 
following is the exact wording:

11.7.2.3.2  The total volume of CLass I, II, and IIIA liquids, including those 
contained in approved storage cabinets and safety cans, shall not exceed 7.57 L 
(2 gal) per 9.29 m2 (100ft2)

(sorry, I couldn't do a superscript!)

Can anyone offer any help on this?

Thanks!

hopper

                          