> >Due to IBM  Health checker report we have to change mode of our  Coupling 
> >facility to non Volatile.. CF is running in a partition on CPC,  shared by 4 
> >z/OS LPARs making it a sysplex. We are enabled for CICSPlex , DB2 Data 
> >sharing, RACF Database Sharing, SMSPlex,  Catalog ECS etc etc.. 
> >
> >Can someone point me in the right direction to measure performance gain (due 
> >to change of CF Mode) , if any.
> >
> >We are RMF, SAS/MXG and BMC Performance assurance (aka Visualiser, Best/1 ) 
> >site.
> >
> 
>         A volatile coupling facility is one in which interruption of the 
> power supply causes loss of the memory contents. You can make the  coupling 
> facility nonvolatile by adding to it an uninterruptible power supply or you 
> can use a battery backup, which uses internal batteries to provide power 
> during an outage.

We are talking about the XCF_CF_STR_NONVOLATILE check, right? Before going to 
the expense of adding a battery or power supply (or - IIRC - just fake it by 
setting the appropriate switch for the CF somewhere in the HMC, which was 
possible in the past), read up carefully what the health check says: It doesn't 
just talk about non-volatility. In essence it talks about non-volatility *and* 
failure isolation. (Read up on both in 'setting up a sysplex'.) Making the CF 
non-volatile will NOT make the exception disappear as long as your CF runs on 
the same *hardware* as any of the z/OSs that use this CF. 

You have the following chances of making this exception disappear:
1. Make sure that no z/OS that uses the CF is on the same hardware as the CF 
(failure isolation) *and* provide the battery to that hardware (non-volatility).
2. Buy a standalone CF (failure isolation) with the appropriate battery 
(non-volatility).
3. Delete this health check and go on as before (just for completeness).

>From the top of my head, structures that would like to have a non-volatile, 
>failure-isolated CF are typically system logger structures. Assuming that you 
>configured them correctly, they will already automatically be duplexing data 
>written to the CF to staging data sets. Which will give you the result you 
>need: In case of power failure to the hardware your z/OS runs on, there is a 
>copy of the data still available somewhere (in this case, staging data sets). 
>You will gain a small benefit in performance because with a failure isolated, 
>non-volatile CF duplexing to staging data sets is no longer necessary for 
>system logger.

Not sure if other structures also request non-volatile, failure isolated CFs.