On 2/28/08 9:31 AM, "Michael Gillett" <[EMAIL PROTECTED]> wrote:
> Has anyone created or discovered a SNMP probe for this model of UPS?
> Or at least how to extract the OIDs? I've tried the probes in the
> upsbundle, and although they work with other Liebert UPS models, for
> some reason not with this particular model.
>
> I've tried SNMPWalking the device but it doesn't return any values,
> just moves to the next device on the Map. Right now the ping/echo
> probe is the only thing that works right with this UPS, but that
> probe doesn't return any useful information except that the device
> has a presence on our network. At the very least I'd like to know
> when the UPS begins to carry the power load for its server room.
Do you have SNMP enabled on the UPS? It may not be enabled by default (it
wasn't on ours). Our Liebert NPower MX 80kVA responds reasonably well to the
Liebert UPS - Open Comms probe, although it returns impossible zero values and
errors in some cases (see partial example below). The unit came with MIB files
on a CD-ROM, and those had to be imported into IM. If you don't have a CD for
your unit, check with your local Liebert rep or dig around on their Web site.
---------------------------
Liebert UPS / OpenComms Web Card Information
Vendor: Liebert Corporation
Model: Npower
Software: 3.120.3
Firmware: V 1.27
Alarm Status: No Alarms Reported
Output Source: Normal
Battery Status: Normal
(100 % Charge, 65535.0 Minutes Left.)
(538.0 Volts; 0.0 Amps.)
Input Status
Line 1: 60.0 Hz; 483 Volts; 20.0 Amps; 0.000 KWatts.
Line 2: 60.0 Hz; 488 Volts; 22.0 Amps; 0.000 KWatts.
Line 3: 60.0 Hz; 486 Volts; 21.5 Amps; 0.000 KWatts.
(3 lines, 3 displayed)
Output Status
Line 1: 60.0 Hz; 119 Volts; 34.7 Amps; 4.000 KWatts; 17 % Load.
Line 2: 60.0 Hz; 120 Volts; 30.9 Amps; 4.000 KWatts; [noSuchName] %
Load.
Line 3: 60.0 Hz; 120 Volts; 28.0 Amps; 3.000 KWatts; [noSuchName] %
Load.
(3 lines, 3 displayed)
Temperature Monitoring
Battery: 0.0 ¡C, 0.0 ¡F,
Ambient: 0.0 ¡C, 0.0 ¡F,
------------------------------
I sent e-mail to [EMAIL PROTECTED] last October to see what can be done about
those zero values and "[noSuchName]" values, but haven't heard anything.
--
Chip Old (Francis E. Old) <[EMAIL PROTECTED]>
Administrator, Network Operations
Baltimore County Public Library
320 York Road
Towson, MD 21204-5179 US
410-887-6180 Office
410-887-2091 FAX
____________________________________________________________________
List archives:
http://www.mail-archive.com/intermapper-talk%40list.dartware.com/
To unsubscribe: send email to: [EMAIL PROTECTED]