Christofer Dutz commented on PLC4X-134:
---------------------------------------

Ah ok ... so if you want rack 0 and slot 2 it should have been "/1/2" at the 
end. However it seems as if Siemens uses rack and slot not directly, but 
instead uses this to calculate the tsapId. I have never had access to a machine 
that didn't accept a connection. So if you found a problem here, we should 
investigate and correct the S7TsapIdEncoder classes. Could you perhaps send us 
a packet capture of a connection (with TIA for example) with that device? That 
would help us a lot ... I think the patch you suggested would completely make 
"rack" and "slot" options obsolete and I think they do have a purpose.

> S7 is terminating the connection during handshake
> -------------------------------------------------
>
>                 Key: PLC4X-134
>                 URL: https://issues.apache.org/jira/browse/PLC4X-134
>             Project: Apache PLC4X
>          Issue Type: Bug
>          Components: Driver-S7
>    Affects Versions: 0.5.0
>            Reporter: Mirko Pohland
>            Priority: Critical
>         Attachments: stack_trace.txt
>
>
> When trying to connect to my S7-300 I get the following error (stack trace 
> attached): 
> {color:#FF0000} org.apache.plc4x.java.api.exceptions.PlcIoException: 
> Connection terminated by remote{color}
> After some debugging I found out that I can fix this issue by doing a small 
> change in S7PlcConnection.java
>  
> From
>         short calledTsapId = S7TsapIdEncoder.encodeS7TsapId(DeviceGroup.OS, 
> 0, 0);
>         short callingTsapId = 
> S7TsapIdEncoder.encodeS7TsapId(DeviceGroup.PG_OR_PC, rack, slot);
> where calledTsapId does not contain rack and slot to
>         short calledTsapId = S7TsapIdEncoder.encodeS7TsapId(DeviceGroup.OS, 
> rack, slot);
>         short callingTsapId = 
> S7TsapIdEncoder.encodeS7TsapId(DeviceGroup.PG_OR_PC, 0, 0);
> Now I can connect to the S7.



--