https://issues.apache.org/jira/browse/PLC4X-182?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17051525#comment-17051525
]
César García commented on PLC4X-182:
------------------------------------
Hi,
1. The modification made to the driver allows the partition of the items by
item size and regrouped according to the size of the PDU.
2. Part of the code for handling long messages was transformed into a Netty
layer, only dedicated to executing point 1.
3. Bits fix requests are made as individual Items, but the partition is made
from the beginning. This makes it easier for each layer in Netty to do only one
thing.
The result of this can be seen in the attached capture in the PLC4X-181
activity.
For version 0.6.1, very long Items (that exceed a PDU) both write and read will
be rejected indicating poor quality.
Waiting for your observations,
Best regards,
> Request split / Message Split
> -----------------------------
>
> Key: PLC4X-182
> URL: https://issues.apache.org/jira/browse/PLC4X-182
> Project: Apache PLC4X
> Issue Type: Improvement
> Components: Driver-S7
> Reporter: César García
> Assignee: César García
> Priority: Major
> Fix For: 0.6.1
>
>
> # A request with many Items is divided within the limits allowed by the size
> of the PDU.
> # If one of the requested Items exceeds the size of the PDU it is trimmed to
> the maximum size of the PDU. The existing code tries to split the message,
> but it fails. This generates an unsafe condition.
> # Rethink the routine for handling long messages, as an additional layer in
> Netty.
--
This message was sent by Atlassian Jira
(v8.3.4#803005)