https://issues.apache.org/jira/browse/PLC4X-279?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17276397#comment-17276397
 ] 

Łukasz Dywicki commented on PLC4X-279:
--------------------------------------

[~fox_pluto] was you able to fetch also amount of connect/disconnect events 
from pool2? I ask cause if we correlate these we know that pool2 is faulty, if 
not then actual issue might be in lower layer. In the runtime {{NioEventLoop}} 
is managed internally by netty.

> nioEventLoopGroup thread proliferation
> --------------------------------------
>
>                 Key: PLC4X-279
>                 URL: https://issues.apache.org/jira/browse/PLC4X-279
>             Project: Apache PLC4X
>          Issue Type: Bug
>          Components: Driver-S7
>    Affects Versions: 0.8.0
>            Reporter: Stefano Bossi
>            Priority: Major
>         Attachments: Screenshot 2021-02-01 at 09.19.07.png, Screenshot 
> 2021-02-01 at 09.20.42.png, Threads total 2021-01-31 at 11.34.15.png, Threads 
> total 2021-02-01 at 09.14.02.png
>
>
> Dear developers,
> I did a stability test with the plc4x 0.8.0 and pool2 library.
> The test is just reading continuously a couple of DataBlock from a S7 Siemens 
> 1200 PLC.
> During the test I have used VisualVM like profiler to inspect the use of the 
> Heap and the threads and I found something strange.
> The test runs for a couple of days and I have sampled the threads in a couple 
> of snapshot found that the number of running nioEventLoopGroup thread 
> increase and doesn't seems to be bounded by a limit.
> These are the total of the Threads of the applications at 2021-01-31 at 
> 11.34.15; the total number is 246 and the number of nioEventLoopGroup is 192
> !Threads total 2021-01-31 at 11.34.15.png|width=568,height=332!
> These are the total of the Threads of the applications at 2021-02-01 at 
> 09.14.02; the total number is 358 and the number of nioEventLoopGroup is 305
> !Threads total 2021-02-01 at 09.14.02.png|width=549,height=309!
>  Form the profiler two of this thread are:
> !Screenshot 2021-02-01 at 09.19.07.png|width=530,height=210!
> !Screenshot 2021-02-01 at 09.20.42.png|width=539,height=271!  
>  
> It seems a leakage and seems a dangerous one. 
> I think the problem is inside the pool2 library but I am note sure. 
> What do you think? 
> Regards,
> S.
>  
>  



--
This message was sent by Atlassian Jira
(v8.3.4#803005)