https://issues.apache.org/jira/browse/PLC4X-341?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17536410#comment-17536410
]
Andy Grebe commented on PLC4X-341:
----------------------------------
Hi Chris,
I was able to get the LINTs working without an issue. However, the STRING
seems to be an issue. When I read a string, I get the following in the command
specific data:
a002ce0f040000007465737400000000...(the 0s at the end are due to the fact that
strings are a set size of 82 BYTEs)
So the 0x02a0, is specifying a string, or structured data type, I can't get
clarification on that with the CIP/EIP documentation I've come across. Then
there are the next two bytes, which I'm hoping designate the structured data
type as string, followed by the actual size of the string. I was able to use
this to get the string read from the response.
So when writing, I used both the current code and modified code based on the
above format[^eipcipstringwrite1.pcapng] to write a string:
a0020100544553540000000000000000... for the current code in plc4x
and
a002ce0f0400000054455354000000000...modified to resemble the packet sent on a
read.
However, both give me a status of 0xFF and extended status of 0x2107, which
from Allen Bradley specifies {_}0x2107{_}. General {_}Error{_}: Data type used
in request does not match the data type of the target tag. The tag name is the
same. I did reach out to support to see if there is an issue with the data, or
if they don't actually support STRING writes. I did attach a wireshark dump
from when I was testing.
Also, what other data types are missing?
Andy
> PLC4J GIP/CIP Read STRING tag returns null w/error
> --------------------------------------------------
>
> Key: PLC4X-341
> URL: https://issues.apache.org/jira/browse/PLC4X-341
> Project: Apache PLC4X
> Issue Type: Bug
> Components: Driver-Ethernet/IP, PLC4J
> Affects Versions: 0.9.1
> Reporter: Andy Grebe
> Priority: Major
> Attachments: eipcipstringread.pcapng, eipcipstringwrite1.pcapng
>
>
> STRING tag reads in plc4j using eip are not returning the string. The error
> returned is:
> java.lang.NullPointerException: Cannot invoke
> "org.apache.plc4x.java.api.value.PlcValue.getString()" because the return
> value of
> "org.apache.plc4x.java.api.messages.PlcReadResponse.getPlcValue(String)" is
> null
> It looks like plc4j is considering it a structure or array. If I read with
> {code:java}
> %MyString[{index}]:STRING:1 {code}
> I can get the individual characters in the string by placing the actual index
> in \{index}. So it knows where to start reading the data from.
> When running a wireshark cap, I can see the returned string in the response
> from the PLC. Attached is a pcap of the transaction.
>
> Code Snippet:
> {code:java}
> try (PlcConnection plcConnection = new
> PlcDriverManager().getConnection("eip://127.0.0.1")) {
> if (!plcConnection.getMetadata().canRead()) {
> logger.error("PLC connection doesn't support reading.");
> return;
> }
> logger.info("PLC connector connected"); // Create a new read request:
> PlcReadRequest.Builder builder = plcConnection.readRequestBuilder();
> logger.info("Created Builder");
> builder.addItem("value-1", "%MyString:STRING:1");
> PlcReadRequest readRequest = builder.build(); // Register a callback
> executed as soon as a response arrives.
> logger.info("Make sync request for PLC data");
> PlcReadResponse readResponse = readRequest.execute().get(5000,
> TimeUnit.MILLISECONDS);
> if (readResponse != null) {
> printPlcResponse(readResponse);
> } else {
> logger.error("An error reading PLC, response is NULL");
> }
> for (String field : readResponse.getFieldNames()){
> rtnArray.add(new PlcReadResponseData(field,
> readResponse.getPlcValue(field).getString()) ); // Exception is
> thrown here
> }
> } catch (PlcConnectionException e) {
> e.printStackTrace();
> } {code}
>
--
This message was sent by Atlassian Jira
(v8.20.7#820007)