StrawberryBlue commented on issue #1212:
URL: https://github.com/apache/plc4x/issues/1212#issuecomment-1958518903
I continued testing, and when I looped read the data, there was an
incomplete message. The test code is as follows
` @Test
public void modbusRtuRead(){
try (PlcConnection connection =
PlcDriverManager.getDefault().getConnectionManager().getConnection(MODBUS_RTU_CONNECT_OPTION))
{
while (true) {
// Check if this connection support reading of data.
if (!connection.getMetadata().isReadSupported()) {
log.error("This connection doesn't support reading.");
return;
}
PlcReadRequest.Builder builder =
connection.readRequestBuilder();
builder.addTagAddress("value-1", "400001:UINT[100]");
PlcReadRequest readRequest = builder.build();
long start = System.currentTimeMillis();
PlcReadResponse response = null;
response = readRequest.execute().get(5000,
TimeUnit.MILLISECONDS);
if (response != null) {
for (String tagName : response.getTagNames()) {
if (response.getResponseCode(tagName) ==
PlcResponseCode.OK) {
int numValues =
response.getNumberOfValues(tagName);
// If it's just one element, output just one
single line.
if (numValues == 1) {
log.info("Value[" + tagName + "]: " +
response.getObject(tagName));
}
// If it's more than one element, output each in
a single row.
else {
log.info("Value[" + tagName + "]:");
for (int i = 0; i < numValues; i++) {
log.info(" - " +
response.getObject(tagName, i));
}
}
}
// Something went wrong, to output an error message
instead.
else {
log.error("Error[" + tagName + "]: " +
response.getResponseCode(tagName).name());
}
}
}
long end = System.currentTimeMillis();
System.out.println(end - start);
Thread.sleep(50);
}
} catch (Exception e) {
throw new RuntimeException(e);
}
}`
After a period of program execution, there may be a half package situation,
The complete response message should be
'0103c8000100000000000000000000000000000000000a000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000064a2ba',
but the program cannot correctly parse the message due to two returns. Should
length verification be added to the modbus return message. The error message is
as follows
`2024-02-22 09:41:33.469 WARN 19404 --- [ntLoopGroup-2-1]
.p.j.s.GeneratedDriverByteToMessageCodec : Error decoding package with content
[0103c8000100000000000000000000000000000000000a00000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000]:
Index 159 out of bounds for length 159
java.lang.ArrayIndexOutOfBoundsException: Index 159 out of bounds for length
159
at
com.github.jinahya.bit.io.ArrayByteInput.read(ArrayByteInput.java:106)
~[bit-io-1.4.3.jar:na]
at
com.github.jinahya.bit.io.DefaultBitInput.read(DefaultBitInput.java:57)
~[bit-io-1.4.3.jar:na]
at
com.github.jinahya.bit.io.AbstractBitInput.unsigned8(AbstractBitInput.java:63)
~[bit-io-1.4.3.jar:na]
at
com.github.jinahya.bit.io.AbstractBitInput.unsigned16(AbstractBitInput.java:92)
~[bit-io-1.4.3.jar:na]
at
com.github.jinahya.bit.io.AbstractBitInput.readInt(AbstractBitInput.java:135)
~[bit-io-1.4.3.jar:na]
at
com.github.jinahya.bit.io.AbstractBitInput.readInt(AbstractBitInput.java:118)
~[bit-io-1.4.3.jar:na]
at
com.github.jinahya.bit.io.AbstractBitInput.readByte(AbstractBitInput.java:106)
~[bit-io-1.4.3.jar:na]
at
org.apache.plc4x.java.spi.generation.ReadBufferByteBased.readSignedByte(ReadBufferByteBased.java:388)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.generation.ReadBuffer.readByte(ReadBuffer.java:44)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.generation.ReadBufferByteBased.readByteArray(ReadBufferByteBased.java:126)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusPDUReadHoldingRegistersResponse.staticParseModbusPDUBuilder(ModbusPDUReadHoldingRegistersResponse.java:112)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusPDU.staticParse(ModbusPDU.java:181)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU.lambda$0(ModbusRtuADU.java:132)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.io.DataReaderComplexDefault.read(DataReaderComplexDefault.java:70)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.io.DataReaderComplexDefault.read(DataReaderComplexDefault.java:61)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple.lambda$0(FieldReaderSimple.java:34)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.FieldCommons.switchParseByteOrderIfNecessary(FieldCommons.java:52)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple.readSimpleField(FieldReaderSimple.java:34)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.fields.FieldReaderFactory.readSimpleField(FieldReaderFactory.java:133)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU.staticParseModbusADUBuilder(ModbusRtuADU.java:129)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusADU.staticParse(ModbusADU.java:117)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusADU.staticParse(ModbusADU.java:103)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.rtu.ModbusRtuDriver.lambda$0(ModbusRtuDriver.java:130)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.decode(GeneratedDriverByteToMessageCodec.java:87)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
io.netty.handler.codec.ByteToMessageCodec$1.decode(ByteToMessageCodec.java:42)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.handler.codec.ByteToMessageDecoder.decodeRemovalReentryProtection(ByteToMessageDecoder.java:529)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.handler.codec.ByteToMessageDecoder.callDecode(ByteToMessageDecoder.java:468)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:290)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:442)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:420)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:412)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1410)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:440)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:420)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:919)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
org.apache.plc4x.java.transport.serial.SerialChannel$SerialNioUnsafe.read(SerialChannel.java:285)
~[plc4j-transport-serial-0.12.0.jar:0.12.0]
at
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:788)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.nio.NioEventLoop.processSelectedKeysPlain(NioEventLoop.java:689)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:652)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:562)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:997)
~[netty-common-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
~[netty-common-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
~[netty-common-4.1.94.Final.jar:4.1.94.Final]
at java.base/java.lang.Thread.run(Thread.java:829) ~[na:na]
2024-02-22 09:41:33.471 WARN 19404 --- [ntLoopGroup-2-1]
.p.j.s.GeneratedDriverByteToMessageCodec : Error decoding package with content
[0000000000000000000000000000000000000000000000000000000000000000000000000000000000000064a2ba]:
Unsupported case for discriminated type parameters [errorFlag=false
functionFlag=0 response=true]
org.apache.plc4x.java.spi.generation.ParseException: Unsupported case for
discriminated type parameters [errorFlag=false functionFlag=0 response=true]
at
org.apache.plc4x.java.modbus.readwrite.ModbusPDU.staticParse(ModbusPDU.java:310)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU.lambda$0(ModbusRtuADU.java:132)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.io.DataReaderComplexDefault.read(DataReaderComplexDefault.java:70)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.io.DataReaderComplexDefault.read(DataReaderComplexDefault.java:61)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple.lambda$0(FieldReaderSimple.java:34)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.FieldCommons.switchParseByteOrderIfNecessary(FieldCommons.java:52)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple.readSimpleField(FieldReaderSimple.java:34)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.codegen.fields.FieldReaderFactory.readSimpleField(FieldReaderFactory.java:133)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU.staticParseModbusADUBuilder(ModbusRtuADU.java:129)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusADU.staticParse(ModbusADU.java:117)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.readwrite.ModbusADU.staticParse(ModbusADU.java:103)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.modbus.rtu.ModbusRtuDriver.lambda$0(ModbusRtuDriver.java:130)
~[plc4j-driver-modbus-0.12.0.jar:0.12.0]
at
org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.decode(GeneratedDriverByteToMessageCodec.java:87)
~[plc4j-spi-0.12.0.jar:0.12.0]
at
io.netty.handler.codec.ByteToMessageCodec$1.decode(ByteToMessageCodec.java:42)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.handler.codec.ByteToMessageDecoder.decodeRemovalReentryProtection(ByteToMessageDecoder.java:529)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.handler.codec.ByteToMessageDecoder.callDecode(ByteToMessageDecoder.java:468)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:290)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
~[netty-codec-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:442)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:420)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:412)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1410)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:440)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:420)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:919)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
org.apache.plc4x.java.transport.serial.SerialChannel$SerialNioUnsafe.read(SerialChannel.java:285)
~[plc4j-transport-serial-0.12.0.jar:0.12.0]
at
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:788)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.nio.NioEventLoop.processSelectedKeysPlain(NioEventLoop.java:689)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:652)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:562)
~[netty-transport-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:997)
~[netty-common-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
~[netty-common-4.1.94.Final.jar:4.1.94.Final]
at
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
~[netty-common-4.1.94.Final.jar:4.1.94.Final]
at java.base/java.lang.Thread.run(Thread.java:829) ~[na:na]`
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: [email protected]