AleiynikovPavel opened a new issue, #1443:
URL: https://github.com/apache/plc4x/issues/1443

   ### What happened?
   
   Error decoding TCP packet after N read requests.
   ## Example code causing the bug
   ### Description
   -  I get an error both on the real device and on the [Modbus Slave 
Simulator](https://www.modbusdriver.com/diagslave.html) running with option `-m 
enc`
   - I **always** get it at the **40th** iteration of the loop presented in the 
code example
   - There is no error if you execute only one request per loop iteration 
(comment out the second request)
   - There are also no errors in `modbus-tcp` mode
   - There is also no error if both the first and second commands request the 
same number of registers
   ### Code
   ```java
   package org.test.plc4j;
   
   import org.apache.plc4x.java.DefaultPlcDriverManager;
   import org.apache.plc4x.java.api.exceptions.PlcConnectionException;
   
   import java.util.concurrent.ExecutionException;
   
   public class Main {
   
       public static void main(String[] args) throws PlcConnectionException {
           var connection = new 
DefaultPlcDriverManager().getConnection("modbus-rtu:tcp://localhost:502");
           for (int i = 0; i < 45; i++) {
               try {
                   connection.readRequestBuilder()
                           .addTagAddress("1", 
"input-register:1[125]").build().execute().get();
               } catch (InterruptedException | ExecutionException e) {
                   System.err.println("Failed command 1 on iteration " + i);
               }
               try {
                   connection.readRequestBuilder()
                           .addTagAddress("1", 
"input-register:1[50]").build().execute().get();
               } catch (InterruptedException | ExecutionException e) {
                   System.err.println("Failed command 2 on iteration " + i);
               }
           }
       }
   
   }
   ```
   ### Output log
   ```bash
   21:49:50.787 [nioEventLoopGroup-2-1] WARN 
org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec -- Error decoding 
package with content 
[0104fa000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000]:
 Index 240 out of bounds for length 240
   java.lang.ArrayIndexOutOfBoundsException: Index 240 out of bounds for length 
240
        at 
com.github.jinahya.bit.io.ArrayByteInput.read(ArrayByteInput.java:106)
        at 
com.github.jinahya.bit.io.DefaultBitInput.read(DefaultBitInput.java:57)
        at 
com.github.jinahya.bit.io.AbstractBitInput.unsigned8(AbstractBitInput.java:63)
        at 
com.github.jinahya.bit.io.AbstractBitInput.unsigned16(AbstractBitInput.java:92)
        at 
com.github.jinahya.bit.io.AbstractBitInput.readInt(AbstractBitInput.java:135)
        at 
com.github.jinahya.bit.io.AbstractBitInput.readInt(AbstractBitInput.java:118)
        at 
com.github.jinahya.bit.io.AbstractBitInput.readByte(AbstractBitInput.java:106)
        at 
org.apache.plc4x.java.spi.generation.ReadBufferByteBased.readSignedByte(ReadBufferByteBased.java:388)
        at 
org.apache.plc4x.java.spi.generation.ReadBuffer.readByte(ReadBuffer.java:44)
        at 
org.apache.plc4x.java.spi.generation.ReadBufferByteBased.readByteArray(ReadBufferByteBased.java:126)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusPDUReadInputRegistersResponse.staticParseModbusPDUBuilder(ModbusPDUReadInputRegistersResponse.java:112)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusPDU.staticParse(ModbusPDU.java:171)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU.lambda$0(ModbusRtuADU.java:132)
        at 
org.apache.plc4x.java.spi.codegen.io.DataReaderComplexDefault.read(DataReaderComplexDefault.java:70)
        at 
org.apache.plc4x.java.spi.codegen.io.DataReaderComplexDefault.read(DataReaderComplexDefault.java:61)
        at 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple.lambda$0(FieldReaderSimple.java:34)
        at 
org.apache.plc4x.java.spi.codegen.FieldCommons.switchParseByteOrderIfNecessary(FieldCommons.java:52)
        at 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple.readSimpleField(FieldReaderSimple.java:34)
        at 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderFactory.readSimpleField(FieldReaderFactory.java:133)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU.staticParseModbusADUBuilder(ModbusRtuADU.java:129)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusADU.staticParse(ModbusADU.java:117)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusADU.staticParse(ModbusADU.java:103)
        at 
org.apache.plc4x.java.modbus.rtu.ModbusRtuDriver.lambda$0(ModbusRtuDriver.java:130)
        at 
org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.decode(GeneratedDriverByteToMessageCodec.java:87)
        at 
io.netty.handler.codec.ByteToMessageCodec$1.decode(ByteToMessageCodec.java:42)
        at 
io.netty.handler.codec.ByteToMessageDecoder.decodeRemovalReentryProtection(ByteToMessageDecoder.java:529)
        at 
io.netty.handler.codec.ByteToMessageDecoder.callDecode(ByteToMessageDecoder.java:468)
        at 
io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:290)
        at 
io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:442)
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:420)
        at 
io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:412)
        at 
io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1410)
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:440)
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:420)
        at 
io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:919)
        at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:166)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:788)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:724)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:650)
        at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:562)
        at 
io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:997)
        at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
        at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
        at java.base/java.lang.Thread.run(Thread.java:833)
   21:49:50.789 [nioEventLoopGroup-2-1] DEBUG 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple -- reading field 
address
   21:49:50.790 [nioEventLoopGroup-2-1] DEBUG 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple -- reading field pdu
   21:49:50.790 [nioEventLoopGroup-2-1] DEBUG 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderDiscriminator -- reading 
field errorFlag
   21:49:50.790 [nioEventLoopGroup-2-1] DEBUG 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderDiscriminator -- reading 
field functionFlag
   21:49:50.790 [nioEventLoopGroup-2-1] WARN 
org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec -- Error decoding 
package with content [00000000000000000000000000f0a3]: Unsupported case for 
discriminated type parameters [errorFlag=false functionFlag=0 response=true]
   org.apache.plc4x.java.spi.generation.ParseException: Unsupported case for 
discriminated type parameters [errorFlag=false functionFlag=0 response=true]
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusPDU.staticParse(ModbusPDU.java:310)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU.lambda$0(ModbusRtuADU.java:132)
        at 
org.apache.plc4x.java.spi.codegen.io.DataReaderComplexDefault.read(DataReaderComplexDefault.java:70)
        at 
org.apache.plc4x.java.spi.codegen.io.DataReaderComplexDefault.read(DataReaderComplexDefault.java:61)
        at 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple.lambda$0(FieldReaderSimple.java:34)
        at 
org.apache.plc4x.java.spi.codegen.FieldCommons.switchParseByteOrderIfNecessary(FieldCommons.java:52)
        at 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderSimple.readSimpleField(FieldReaderSimple.java:34)
        at 
org.apache.plc4x.java.spi.codegen.fields.FieldReaderFactory.readSimpleField(FieldReaderFactory.java:133)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU.staticParseModbusADUBuilder(ModbusRtuADU.java:129)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusADU.staticParse(ModbusADU.java:117)
        at 
org.apache.plc4x.java.modbus.readwrite.ModbusADU.staticParse(ModbusADU.java:103)
        at 
org.apache.plc4x.java.modbus.rtu.ModbusRtuDriver.lambda$0(ModbusRtuDriver.java:130)
        at 
org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.decode(GeneratedDriverByteToMessageCodec.java:87)
        at 
io.netty.handler.codec.ByteToMessageCodec$1.decode(ByteToMessageCodec.java:42)
        at 
io.netty.handler.codec.ByteToMessageDecoder.decodeRemovalReentryProtection(ByteToMessageDecoder.java:529)
        at 
io.netty.handler.codec.ByteToMessageDecoder.callDecode(ByteToMessageDecoder.java:468)
        at 
io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:290)
        at 
io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:442)
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:420)
        at 
io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:412)
        at 
io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1410)
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:440)
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:420)
        at 
io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:919)
        at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:166)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:788)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:724)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:650)
        at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:562)
        at 
io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:997)
        at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
        at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
        at java.base/java.lang.Thread.run(Thread.java:833)
   Failed command 1 on iteration 20
   ```
   ### Full log file
   - Full log of the program: 
[out.txt](https://github.com/apache/plc4x/files/14500068/out.txt)
   
   ### Version
   
   v0.12.0
   
   ### Programming Languages
   
   - [X] plc4j
   - [ ] plc4go
   - [ ] plc4c
   - [ ] plc4net
   
   ### Protocols
   
   - [ ] AB-Ethernet
   - [ ] ADS /AMS
   - [ ] BACnet/IP
   - [ ] CANopen
   - [ ] DeltaV
   - [ ] DF1
   - [ ] EtherNet/IP
   - [ ] Firmata
   - [ ] KNXnet/IP
   - [X] Modbus
   - [ ] OPC-UA
   - [ ] S7


-- 
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.

To unsubscribe, e-mail: [email protected]

For queries about this service, please contact Infrastructure at:
[email protected]

Reply via email to