splatch commented on issue #1472:
URL: https://github.com/apache/plc4x/issues/1472#issuecomment-2032030176

   > Thanks for your cooperation. I have seen other issues related to opc ua 
dealing with stale mode / tokens #1364 still not fully resolved. There is no 
rush to get these issues sorted out, specially the connection issue that I have 
mentionned and which seems to be also an issue in v.0.12.0 as stated in the 
link provided above.
   
   To throw some context in above issue - I've found cause for missing 
subscriptions, however I've also found a lower level issue related to renewing 
of OPC-UA security token which I couldn't fix yet. I have to book for that at 
least two-three days to understand logic which we should build, and test it 
with software and hardware based servers.


-- 