lzago opened a new issue, #1733:
URL: https://github.com/apache/plc4x/issues/1733

   ### What would you like to happen?
   
   Actually only addresses of this kind: ` %MX1.0:BOOL` to read from Merker 
Type of area  are accepted. 
   Becase of the regexp:
   
"^%(?<memoryArea>.)(?<transferSizeCode>[XBWD]?)(?<byteOffset>\\d{1,7})(.(?<bitOffset>[0-7]))?:(?<dataType>(S5)?[a-zA-Z_]+)(\\[(?<numElements>\\d+)])?"
   
   on S7Tag class. 
   So with the byteOffset only between 1 and 7. 
   When it's common to use larger offset. I can read addresses %M1000.0 BOOL 
using Snap7 on the same PLC. 
   I didn't open a bug because probably it comes from a a good practice, but i 
open feature request at least to open a discussion why not to support a 
different offset. 
   
   ### Programming Languages
   
   - [X] plc4j
   - [ ] plc4go
   - [ ] plc4c
   - [ ] plc4net
   
   ### Protocols
   
   - [ ] AB-Ethernet
   - [ ] ADS /AMS
   - [ ] BACnet/IP
   - [ ] CANopen
   - [ ] DeltaV
   - [ ] DF1
   - [ ] EtherNet/IP
   - [ ] Firmata
   - [ ] KNXnet/IP
   - [ ] Modbus
   - [ ] OPC-UA
   - [X] S7


-- 