On 12/27/2010 03:36 PM, ahmet erkan wrote:
>"I did try using a GFCI on the engine room circuit but the environment in the ER was too damp and it wouldn't hold.
>I have not tried it elsewhere but I don't know why they wouldn't work.
>Even though the neutral is floating (on my boat), all the non-current carrying metal parts are still grounded."

With a "floating Neutral", the GFCI is going to detect a current from hot terminal through a person to earth and trip open only if the neutral insulation has also broken down to ground, similarly GFCI is going to detect a current from neutral through a person to earth and open only if the hot line insulation has also broken down to earth. (I believe
Norm has also said this in different words)
If one wants to use GFCI devices with a floating Neutral, I suggest he/she (so PC) connects a 1uF capacitor from the hot line to ship's ground and another 1uF capacitor from the neutral to the ships ground. Both capacitors should be connected to the line side of the GFCI device. (ie: at the 120V secondary of your shielded isolation transformer preferably close to the transformer for noise attenuation purposes) "60V is safer than 120V" in fact the 48V used by the phone company is actually the terminal voltage of a 48V rated battery that is typically at 55V and could go to 60V during equalize. At the phone company we routinely worked on the 48V live equipment and touched the negative terminal (positive terminal is grounded for galvanic
corrosion prevention) without worrying about getting electrocuted.
So there you are, a +/-60Vac ships system with a GFCI protection device that will trip if there is more than 5mA imbalance between the hot or neutral currents and a little safer than your floating Neutral system. The imbalance will occur and interrupt the circuit either during a "heavy wet contact" by the user or if there is a fault in the system. The GFCI used in a grounded neutral system cannot detect Neutral to Ground type ground faults reliably due to lack of a supply to drive the current but the +/- 60V system _should_ detect either Hot to ground or Neutral
to ground insulation failures equally reliably. (Do test anyway)
The capacitors should also work in tandem with the shield during lightning storms and provide common mode attenuation to voltage spikes in the order of 120dB. The capacitors should also work in tandem with the leakage inductance of the isolation transformer and provide normal mode attenuation to voltage spikes proportional to
frequency of the disturbance.
Again, test for proper functionality of any system before relying on it for safety. This method of wiring is just a paper design at this time and has not been verified, I can verify using my isolation transformer and a GFCI receptacle or a CB from Home Depot and provide the results to the list if anyone wants
to implement it?
BTW who is Dr. Oz? A friend of George Orwell? I learn so many things on this list.
Fair winds
S/V 8827
Ahmet

------------------------------------------------------------------------
From: banders...@earthlink.net
To: liveaboard@liveaboardonline.com
Date: Sat, 25 Dec 2010 17:13:30 -0500
Subject: Re: [Liveaboard] GALVANIC ISOLATOR


See Annotations Below
Norm
S/V Bandersnatch
Lying Julington Creek FL
N30 07.68 W081 38.47

    ----- Original Message -----
    *From:* ahmet erkan <mailto:ameter...@hotmail.com>
    *To: *liveabo...@liveaboardonline.com
    <mailto:liveaboard@liveaboardonline.com>
    *Sent:* 12/20/2010 11:04:05 PM
    *Subject:* Re: [Liveaboard] GALVANIC ISOLATOR

    Hi Norm,
    I am not sure if your questions have already been answered by the
    list but let me make an attempt anyway.

    You asked :
    _"would you please address the issue of connecting (or not
    connecting) the ac neutral to earth."_
    IMO not connecting the ac neutral to earth would make
    the electrical system safe for the user making accidental contact
    with a hot conductor. However if the user begins to ignore the
    basic safety rules and becomes complacent about touching hot
    conductors he/she will be at the mercy of the system being fault
    free. Therefore a system with an isolated neutral ought to be
    checked frequently (preferably automatically) to verify all the
    current carrying conductors are indeed isolated from the chassis.
    Another shortcoming of the ungrounded neutral is you cannot use
    GFCI circuit breakers.
    One other shortcoming may be the increased vulnerability of your
    electronics to lightning! . The isolation transformer that is
    providing the floating secondary neutral should be shielded
    (preferably both primary and secondary shields) and the shields
    should be hardwired to earth.
    Norm - Yes, I agree (and stated) that a way to check for ground
    faults would be a Good Thing.  Even a simple light bulb or meter.
    There is a shield on my isolation transformer between the windings
    and it is grounded to ship's ground.
    I did try using a GFCI on the engine room circuit but the
    environment in the ER was too damp and it wouldn't hold.  I have
    not tried it elsewhere but I don't know why they wouldn't work.
    Even though the neutral is floating (on my boat), all the
    non-current carrying metal parts are still grounded.
    From what I understand about lightening damage it is small
    voltages inside sensitive electronics induced by the nearby heavy
    current flows from lightening that does the most damage.

    You asked :
    _"I believe in the US power that comes into a house is from a
    center tapped secondary winding in the pole transformer which
    delivers 240 vac at the ends of the coil and the neutral comes
    from the center tap.  The grounding of the neutral is only added
in the house's breaker box by the neutral/grounding jumper wire. Correct me if I am mistaken."_
    Correct, except I have never seen a jumper wire. The
    panels usually have a long aluminum block bolted to the chassis
    and it has a bunch of screw terminals for both neutral and ground
    wires.  US house wiring code requires both neutral (white) and
    ground (green) wires to be terminated to the chassis of the
    distribution panel/circuit breaker box. The chassis of the
    distribution panel is also routed (with a green wire) to a ground
    rod or a buried water pipe. I remember some Canadian folks on the
    list freaking out when they heard white neutral and green ground
    wires are bonded at the chassis of the panel but this is the way
    it is, and it makes sense to us.
    Norm - My memory (such as it is) tells me that  the neutral
    terminal block in the US is insulated, the grounding block not
    insulated, and there is a wire connecting the two.  But I have
    made a note on my "To Do" list to have a look in a breaker box the
    next time I am in Lowes or Home Depot.

    You asked :
    _"I seem to have read that the European electrical system has
    ungrounded neutrals.  Is this true or not?"
    _In Turkey the houses are wired to one phase of the 220V Wye pole
    transformers with a pair of copper wires. One wire is hot and it
    has insulation, the other wire is the neutral and it is a bare
    copper conductor. The bare wire is bonded to the steel pipes that
    bring water to the house. The metal surfaces of the appliances are
    bonded to the bare neutral with a jumper and this jumper may be
    opened by the electrician to test the appliance for leakage. I
    believe the newer houses are using an insulated neutral and a bare
    ground wire so that GFCI devices can be used. The chassis to
    neutral jumper on the appliances are removed to be able to use the
    GFCI devices in bathrooms.

    Cheers
    Ahmet

    Norm - Thank you for the great information about how it is done in
    Turkey.  It sounds safe to me and I'd bet Dr. Oz would approve it too.


http://www.doctoroz.com/

Dr Oz has a USA TV program and gives medical advice. He's rather popular these days.
_______________________________________________
Liveaboard mailing list
Liveaboard@liveaboardonline.com
To adjust your membership settings over the web 
http://liveaboardonline.com/mailman/listinfo/liveaboard
To subscribe send an email to liveaboard-j...@liveaboardonline.com

To unsubscribe send an email to liveaboard-le...@liveaboardonline.com
The archives are at http://www.liveaboardonline.com/pipermail/liveaboard/