Hi,

I totally agree that solar is a very potential technology. Need enough 
batteries to get through the night though. :-)

And, did i mention my box is in a basement? 

But by all means, post that link here when you regoogle it.

rgds,

Reinier Battenberg
Director
Mountbatten Ltd.
+256 782 801 749
www.mountbatten.net

Be a professional website builder: www.easysites.ug


On Thursday 24 September 2009 12:52:10 Dennis M S wrote:
> Hi Renier,
> I think it would help volumes if you tried a solar solution...a base
> package which should be @ 500k Ush should be adequate to run ur
> server, i did come across a unique DIY circuit where UPS's where
> rigged upto a solar cell...i will mail u d link when i stumple upon it
> again ASAP.
> Dennis M S
> Xcard consulting
>
> On 9/22/09, [email protected] <[email protected]> wrote:
> > Send LUG mailing list submissions to
> >     [email protected]
> >
> > To subscribe or unsubscribe via the World Wide Web, visit
> >     http://kym.net/mailman/listinfo/lug
> > or, via email, send a message with subject or body 'help' to
> >     [email protected]
> >
> > You can reach the person managing the list at
> >     [email protected]
> >
> > When replying, please edit your Subject line so it is more specific
> > than "Re: Contents of LUG digest..."
> >
> >
> > Today's Topics:
> >
> >    1. UPS's (Reinier Battenberg)
> >    2. Re: UPS's (Chris Wilson)
> >    3. Re: UPS's (Reinier Battenberg)
> >    4. Re: UPS's (Benoit Marquis)
> >    5. Re: UPS's (Chris Wilson)
> >    6. Re: UPS's (Reinier Battenberg)
> >
> >
> > ----------------------------------------------------------------------
> >
> > Message: 1
> > Date: Tue, 22 Sep 2009 14:16:15 +0300
> > From: Reinier Battenberg <[email protected]>
> > Subject: [LUG] UPS's
> > To: Linux Users Group Uganda <[email protected]>
> > Message-ID: <[email protected]>
> > Content-Type: text/plain;  charset="us-ascii"
> >
> > Hi,
> >
> > I have a bit of a problem with power. I am in a sort of
> > in-the-middle-of-a-real fix stage, so i know my solution isn't perfect.
> > But within its not-perfectness, here are my issues:
> >
> >
> > - My server pulls max 650W in an environment where power goes off for a
> > few seconds-30 seconds regularly. Initially I had a Smart-UPS 750 that
> > was able to deal with these intervals, with one exception.
> >  I have apcupsd running as a deamon and the system will in worst cases
> > shutdown when there is X amount of time left in the batteries. The BIOS
> > is configured to start up when power returns.
> > Problem is: when power returns while the system is shutting down, the
> > system seems to stay off. The BIOS never gets an event, so just shuts
> > down the computer. Shutting down takes about 3 minutes, which is quite a
> > lot. So, first question, how do you tell a shutting down machine that
> > power is back, and it is not shutting down anymore, but rebooting?
> >
> >
> > Secondly, we dont want these reboots. I can't buy an inverter with proper
> > batteries, so I bought a second UPS ( RS 1500) , and placed it in series
> > with
> > the first one. Its a bit cheaper, so i placed it before the SmartUPS, and
> > keep that one connected to the server over USB (and AC).
> >
> > This new UPS is not doing its job. If power goes off, it does switch to
> > batteries, but the Smart UPS that it is feeding in to, immediatly
> > switches to
> > batteries, too. I ran a few tests:
> >
> > With a disconnected RS1500 (no AC in)
> > - Connect the RS1500 to a moniter, and the monitor works.
> > - Connect the RS1500 to the second power-unit of the server. The led
> > light on
> > the server goes on, but on the server-side the power cable makes a funny
> > sizzling noise.
> > - Connect the RS1500 to the Smart-UPS, the smart-UPS does not charge from
> > the
> > RS1500 batteries, and you do hear the sizzling sound on the Smart-UPS
> > side. Also, the Smart-UPS indicates it has lost its power-source and it
> > is running from batteries.
> > - The orange LED is lit on the RS1500, which means, we are on battery
> > now. There is no indication there is an overload.
> >
> > Plug the RS1500 in the grid
> > - Light goes green, and the sizzling sound disappears.
> >
> > Question: is my RS1500 actually helping my Smart-UPS to feed the server
> > with power? (and do i just need to add more batteries?) Or do i have a
> > problem?
> >
> >
> >
> >
> > The smart-UPS:
> > http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA750I
> >
> > The not-so smart one:
> > http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=
> >BR1500I&tab=compare
> >
> >
> >
> > rgds,
> >
> > Reinier Battenberg
> > Director
> > Mountbatten Ltd.
> > +256 782 801 749
> > www.mountbatten.net
> >
> > Be a professional website builder: www.easysites.ug
> >
> >
> >
> >
> > ------------------------------
> >
> > Message: 2
> > Date: Tue, 22 Sep 2009 12:45:35 +0100 (BST)
> > From: Chris Wilson <[email protected]>
> > Subject: Re: [LUG] UPS's
> > To: Linux Users Group Uganda <[email protected]>
> > Message-ID:
> >     <alpine.deb.1.00.0909221240210.7...@fen-ndiyo2.fen.aptivate.org.fen.apti
> >vate.org>
> >
> > Content-Type: TEXT/PLAIN; charset=US-ASCII
> >
> > Hi Reinier,
> >
> > On Tue, 22 Sep 2009, Reinier Battenberg wrote:
> >> I have apcupsd running as a deamon and the system will in worst cases
> >> shutdown when there is X amount of time left in the batteries. The BIOS
> >> is configured to start up when power returns. Problem is: when power
> >> returns while the system is shutting down, the system seems to stay off.
> >> The BIOS never gets an event, so just shuts down the computer. Shutting
> >> down takes about 3 minutes, which is quite a lot. So, first question,
> >> how do you tell a shutting down machine that power is back, and it is
> >> not shutting down anymore, but rebooting?
> >
> > You need to use a UPS daemon that can tell the UPS to initiate a timed
> > (delayed) shutdown, and that does this automatically when it initiates a
> > software shutdown. This will cause the UPS to force a power cycle of the
> > server, bringing it back online. NUT does this, for example.
> >
> >> Secondly, we dont want these reboots. I can't buy an inverter with
> >> proper batteries, so I bought a second UPS ( RS 1500) , and placed it in
> >> series with the first one. Its a bit cheaper, so i placed it before the
> >> SmartUPS, and keep that one connected to the server over USB (and AC).
> >>
> >> This new UPS is not doing its job. If power goes off, it does switch to
> >> batteries, but the Smart UPS that it is feeding in to, immediatly
> >> switches to batteries, too.
> >
> > Chaining UPSes is generally considered a bad idea. APC recommends against
> > it. Most likely, the power quality emitted by the first UPS is not enough
> > to satisfy the second that the mains power is OK, so the second switches
> > to battery too.
> >
> >> I ran a few tests:
> >>
> >> With a disconnected RS1500 (no AC in)
> >> - Connect the RS1500 to a moniter, and the monitor works.
> >> - Connect the RS1500 to the second power-unit of the server. The led
> >> light on
> >> the server goes on, but on the server-side the power cable makes a funny
> >> sizzling noise.
> >
> > Nice :) Probably the server's PSU has little or no PFC and so its current
> > draw is not proportional to voltage, causing a huge inductor in the UPS
> > to vibrate violently (and eventually self-destruct or tear itself off the
> > motherboard).
> >
> >> - Connect the RS1500 to the Smart-UPS, the smart-UPS does not charge
> >> from the
> >> RS1500 batteries, and you do hear the sizzling sound on the Smart-UPS
> >> side.
> >> Also, the Smart-UPS indicates it has lost its power-source and it is
> >> running
> >> from batteries.
> >> - The orange LED is lit on the RS1500, which means, we are on battery
> >> now.
> >>
> >> There is no indication there is an overload.
> >
> > That's because the Smart-UPS is not pulling any power from it.
> >
> >> Plug the RS1500 in the grid
> >> - Light goes green, and the sizzling sound disappears.
> >>
> >> Question: is my RS1500 actually helping my Smart-UPS to feed the server
> >> with
> >> power? (and do i just need to add more batteries?) Or do i have a
> >> problem?
> >
> > No and yes.
> >
> > My advice would be to rip the batteries out of the RS 1500 and chain them
> > in parallel with the batteries of the Smart-UPS, by hanging wires out of
> > the side of the UPS case.
> >
> > Cheers, Chris.
> > --
> > Aptivate | http://www.aptivate.org | Phone: +44 1223 760887
> > The Humanitarian Centre, Fenner's, Gresham Road, Cambridge CB1 2ES
> >
> > Aptivate is a not-for-profit company registered in England and Wales
> > with company number 04980791.
> >
> >
> > ------------------------------
> >
> > Message: 3
> > Date: Tue, 22 Sep 2009 15:48:06 +0300
> > From: Reinier Battenberg <[email protected]>
> > Subject: Re: [LUG] UPS's
> > To: Linux Users Group Uganda <[email protected]>
> > Message-ID: <[email protected]>
> > Content-Type: text/plain;  charset="iso-8859-1"
> >
> > Hi Chris,
> >
> > Not sure that was what I wanted to hear.
> >
> > Second alternative I have is buying an APC batterypack for the RS1500.
> > That would give me 15 more minute which is enough time for the gennie to
> > kick in.
> >
> > Does anyone know a place in town where they would have something advanced
> > as this battery pack?
> >
> > http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BR24BP
> >
> >
> > (looking at the instruction manuals for the 2 UPSs i have, i just dont
> > see how
> > I am going to fit the batteries together.)
> >
> > rgds,
> >
> > Reinier Battenberg
> > Director
> > Mountbatten Ltd.
> > +256 782 801 749
> > www.mountbatten.net
> >
> > Be a professional website builder: www.easysites.ug
> >
> > On Tuesday 22 September 2009 14:45:35 Chris Wilson wrote:
> >> Hi Reinier,
> >>
> >> On Tue, 22 Sep 2009, Reinier Battenberg wrote:
> >> > I have apcupsd running as a deamon and the system will in worst cases
> >> > shutdown when there is X amount of time left in the batteries. The
> >> > BIOS is configured to start up when power returns. Problem is: when
> >> > power returns while the system is shutting down, the system seems to
> >> > stay off. The BIOS never gets an event, so just shuts down the
> >> > computer. Shutting down takes about 3 minutes, which is quite a lot.
> >> > So, first question, how do you tell a shutting down machine that power
> >> > is back, and it is not shutting down anymore, but rebooting?
> >>
> >> You need to use a UPS daemon that can tell the UPS to initiate a timed
> >> (delayed) shutdown, and that does this automatically when it initiates a
> >> software shutdown. This will cause the UPS to force a power cycle of the
> >> server, bringing it back online. NUT does this, for example.
> >>
> >> > Secondly, we dont want these reboots. I can't buy an inverter with
> >> > proper batteries, so I bought a second UPS ( RS 1500) , and placed it
> >> > in series with the first one. Its a bit cheaper, so i placed it before
> >> > the SmartUPS, and keep that one connected to the server over USB (and
> >> > AC).
> >> >
> >> > This new UPS is not doing its job. If power goes off, it does switch
> >> > to batteries, but the Smart UPS that it is feeding in to, immediatly
> >> > switches to batteries, too.
> >>
> >> Chaining UPSes is generally considered a bad idea. APC recommends
> >> against it. Most likely, the power quality emitted by the first UPS is
> >> not enough to satisfy the second that the mains power is OK, so the
> >> second switches to battery too.
> >>
> >> > I ran a few tests:
> >> >
> >> > With a disconnected RS1500 (no AC in)
> >> > - Connect the RS1500 to a moniter, and the monitor works.
> >> > - Connect the RS1500 to the second power-unit of the server. The led
> >> > light on the server goes on, but on the server-side the power cable
> >> > makes
> >> > a funny sizzling noise.
> >>
> >> Nice :) Probably the server's PSU has little or no PFC and so its
> >> current draw is not proportional to voltage, causing a huge inductor in
> >> the UPS to vibrate violently (and eventually self-destruct or tear
> >> itself off the motherboard).
> >>
> >> > - Connect the RS1500 to the Smart-UPS, the smart-UPS does not charge
> >> > from
> >> > the RS1500 batteries, and you do hear the sizzling sound on the
> >> > Smart-UPS
> >> > side. Also, the Smart-UPS indicates it has lost its power-source and
> >> > it is running from batteries.
> >> > - The orange LED is lit on the RS1500, which means, we are on battery
> >> > now. There is no indication there is an overload.
> >>
> >> That's because the Smart-UPS is not pulling any power from it.
> >>
> >> > Plug the RS1500 in the grid
> >> > - Light goes green, and the sizzling sound disappears.
> >> >
> >> > Question: is my RS1500 actually helping my Smart-UPS to feed the
> >> > server with power? (and do i just need to add more batteries?) Or do i
> >> > have a problem?
> >>
> >> No and yes.
> >>
> >> My advice would be to rip the batteries out of the RS 1500 and chain
> >> them in parallel with the batteries of the Smart-UPS, by hanging wires
> >> out of the side of the UPS case.
> >>
> >> Cheers, Chris.
> >
> > ------------------------------
> >
> > Message: 4
> > Date: Tue, 22 Sep 2009 15:41:13 +0200
> > From: Benoit Marquis <[email protected]>
> > Subject: Re: [LUG] UPS's
> > To: Linux Users Group Uganda <[email protected]>
> > Message-ID:
> >     <[email protected]>
> > Content-Type: text/plain; charset="iso-8859-1"
> >
> > hum,
> > maybe it is about sensitivity, I think your RS is not giving enough good
> > quality power to your smart one ...
> > you can try is to lower the sensitivity value, can't remember the name of
> > the parameter
> > sensitivity ? :-)
> > there was some smthg like H,M,L value for it ...
> >
> > reinier : of course you try this at your own risk ! :-)
> >
> >
> > 2009/9/22 Reinier Battenberg <[email protected]>
> >
> >> Hi,
> >>
> >> I have a bit of a problem with power. I am in a sort of
> >> in-the-middle-of-a-real fix stage, so i know my solution isn't perfect.
> >> But
> >> within its not-perfectness, here are my issues:
> >>
> >>
> >> - My server pulls max 650W in an environment where power goes off for a
> >> few
> >> seconds-30 seconds regularly. Initially I had a Smart-UPS 750 that was
> >> able
> >> to deal with these intervals, with one exception.
> >>  I have apcupsd running as a deamon and the system will in worst cases
> >> shutdown when there is X amount of time left in the batteries. The BIOS
> >> is configured to start up when power returns.
> >> Problem is: when power returns while the system is shutting down, the
> >> system
> >> seems to stay off. The BIOS never gets an event, so just shuts down the
> >> computer. Shutting down takes about 3 minutes, which is quite a lot. So,
> >> first question, how do you tell a shutting down machine that power is
> >> back,
> >> and it is not shutting down anymore, but rebooting?
> >>
> >>
> >> Secondly, we dont want these reboots. I can't buy an inverter with
> >> proper batteries, so I bought a second UPS ( RS 1500) , and placed it in
> >> series with
> >> the first one. Its a bit cheaper, so i placed it before the SmartUPS,
> >> and keep that one connected to the server over USB (and AC).
> >>
> >> This new UPS is not doing its job. If power goes off, it does switch to
> >> batteries, but the Smart UPS that it is feeding in to, immediatly
> >> switches to
> >> batteries, too. I ran a few tests:
> >>
> >> With a disconnected RS1500 (no AC in)
> >> - Connect the RS1500 to a moniter, and the monitor works.
> >> - Connect the RS1500 to the second power-unit of the server. The led
> >> light on
> >> the server goes on, but on the server-side the power cable makes a funny
> >> sizzling noise.
> >> - Connect the RS1500 to the Smart-UPS, the smart-UPS does not charge
> >> from the
> >> RS1500 batteries, and you do hear the sizzling sound on the Smart-UPS
> >> side.
> >> Also, the Smart-UPS indicates it has lost its power-source and it is
> >> running
> >> from batteries.
> >> - The orange LED is lit on the RS1500, which means, we are on battery
> >> now. There is no indication there is an overload.
> >>
> >> Plug the RS1500 in the grid
> >> - Light goes green, and the sizzling sound disappears.
> >>
> >> Question: is my RS1500 actually helping my Smart-UPS to feed the server
> >> with
> >> power? (and do i just need to add more batteries?) Or do i have a
> >> problem?
> >>
> >>
> >>
> >>
> >> The smart-UPS:
> >> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA750I
> >>
> >> The not-so smart one:
> >>
> >> http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku
> >>=BR1500I&tab=compare
> >>
> >>
> >>
> >> rgds,
> >>
> >> Reinier Battenberg
> >> Director
> >> Mountbatten Ltd.
> >> +256 782 801 749
> >> www.mountbatten.net
> >>
> >> Be a professional website builder: www.easysites.ug
> >>
> >>
> >> _______________________________________________
> >> LUG mailing list
> >> [email protected]
> >> http://kym.net/mailman/listinfo/lug
> >> %LUG is generously hosted by INFOCOM http://www.infocom.co.ug/
> >>
> >> The above comments and data are owned by whoever posted them (including
> >> attachments if any). The List's Host is not responsible for them in any
> >> way.
> >> ---------------------------------------
> >
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL:
> > http://orion.kym.net/pipermail/lug/attachments/20090922/6a7a9441/attachme
> >nt.html
> >
> > ------------------------------
> >
> > Message: 5
> > Date: Tue, 22 Sep 2009 14:59:18 +0100 (BST)
> > From: Chris Wilson <[email protected]>
> > Subject: Re: [LUG] UPS's
> > To: Linux Users Group Uganda <[email protected]>
> > Message-ID:
> >     <alpine.deb.1.00.0909221453570.7...@fen-ndiyo2.fen.aptivate.org.fen.apti
> >vate.org>
> >
> > Content-Type: TEXT/PLAIN; charset=US-ASCII
> >
> > On Tue, 22 Sep 2009, Reinier Battenberg wrote:
> >> Not sure that was what I wanted to hear.
> >>
> >> Second alternative I have is buying an APC batterypack for the RS1500.
> >> That would give me 15 more minute which is enough time for the gennie to
> >> kick in.
> >>
> >> Does anyone know a place in town where they would have something
> >> advanced as this battery pack?
> >>
> >> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BR24BP
> >>
> >>
> >> (looking at the instruction manuals for the 2 UPSs i have, i just dont
> >> see how I am going to fit the batteries together.)
> >
> > I assume that neither the RS 1500 nor your Smart-UPS is expandable. In
> > that case you would need to do some soldering to add more batteries to
> > them.  It won't be in the manuals, they don't want you to do this, they'd
> > rather that you buy a big, shiny, expandable UPS. But if you're careful
> > about battery voltages and polarities, and the UPS can handle the load of
> > the attached machines you can add more batteries to it fairly easily.
> >
> > Cheers, Chris.
> > --
> > Aptivate | http://www.aptivate.org | Phone: +44 1223 760887
> > The Humanitarian Centre, Fenner's, Gresham Road, Cambridge CB1 2ES
> >
> > Aptivate is a not-for-profit company registered in England and Wales
> > with company number 04980791.
> >
> >
> > ------------------------------
> >
> > Message: 6
> > Date: Tue, 22 Sep 2009 17:05:18 +0300
> > From: Reinier Battenberg <[email protected]>
> > Subject: Re: [LUG] UPS's
> > To: Linux Users Group Uganda <[email protected]>
> > Message-ID: <[email protected]>
> > Content-Type: text/plain;  charset="iso-8859-1"
> >
> > Hi,
> >
> > the BR24BP is indeed an expansion of the RS. Not for just 5 minutes, but
> > for 20. That is quite neat. It comes with a socket & plug system, rather
> > than a wires-hanging-out-soldering system.
> >
> > Last time I soldered was in secondary.
> >
> > rgds,
> >
> > Reinier Battenberg
> > Director
> > Mountbatten Ltd.
> > +256 782 801 749
> > www.mountbatten.net
> >
> > Be a professional website builder: www.easysites.ug
> >
> > On Tuesday 22 September 2009 16:59:18 Chris Wilson wrote:
> >> On Tue, 22 Sep 2009, Reinier Battenberg wrote:
> >> > Not sure that was what I wanted to hear.
> >> >
> >> > Second alternative I have is buying an APC batterypack for the RS1500.
> >> > That would give me 15 more minute which is enough time for the gennie
> >> > to kick in.
> >> >
> >> > Does anyone know a place in town where they would have something
> >> > advanced as this battery pack?
> >> >
> >> > http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BR24BP
> >> >
> >> >
> >> > (looking at the instruction manuals for the 2 UPSs i have, i just dont
> >> > see how I am going to fit the batteries together.)
> >>
> >> I assume that neither the RS 1500 nor your Smart-UPS is expandable. In
> >> that case you would need to do some soldering to add more batteries to
> >> them.  It won't be in the manuals, they don't want you to do this,
> >> they'd rather that you buy a big, shiny, expandable UPS. But if you're
> >> careful about battery voltages and polarities, and the UPS can handle
> >> the load of the attached machines you can add more batteries to it
> >> fairly easily.
> >>
> >> Cheers, Chris.
> >
> > ------------------------------
> >
> > _______________________________________________
> > LUG mailing list
> > [email protected]
> > http://kym.net/mailman/listinfo/lug
> >
> >
> > End of LUG Digest, Vol 61, Issue 46
> > ***********************************


_______________________________________________
LUG mailing list
[email protected]
http://kym.net/mailman/listinfo/lug
%LUG is generously hosted by INFOCOM http://www.infocom.co.ug/

The above comments and data are owned by whoever posted them (including 
attachments if any). The List's Host is not responsible for them in any way.
---------------------------------------

Reply via email to