Dear Mr.Ray, 

I have a problem with load flow solution of particular case file. Here I
am attaching the case file with the mail. 

In my case file, I created some faults in the network(Branches (9,10)
(10,11) and (11,12) are turned 'off') such that the load at bus 10 is
not supplied.
when I run the powerflow....runpf('mycase1'), The solution looks like as
follows

================================================================================
|     Bus Data                                                         
       |
================================================================================
 Bus      Voltage          Generation             Load        
  #   Mag(pu) Ang(deg)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)
----- ------- --------  --------  --------  --------  --------
    1  1.000    0.000     22.85      7.35       -         -   
    2  0.969   -2.611       -         -        3.31      1.79 
    3  0.960   -2.776       -         -        2.13      1.15 
    4  0.946   -3.844       -         -        2.56      1.38 
    5  0.963   -2.751       -         -        0.93      0.50 
    6  0.962   -2.776       -         -         -         -   
    7  0.961   -2.784       -         -         -         -   
    8  0.957   -3.023       -         -        2.07      1.12 
    9  0.948   -3.901       -         -        2.42      1.31 
   10    NaN      NaN       -         -        1.26      0.68 
   11    NaN      NaN       -         -         -         -   
   12  0.981   -1.623       -         -        1.33      0.78 
   13  0.992   -0.969       -         -        5.34      2.99 
   14  1.000   -1.524      3.00      7.99       -         -   
   15  0.982   -1.536       -         -        2.67      1.44 
   16  1.000   -1.524       -         -         -         -   
   17  0.972   -1.819       -         -         -         -   
   18  0.964   -2.192       -         -        2.67      1.44 
                        --------  --------  --------  --------
               Total:     25.85     15.34     26.69     14.58



Does this mean we can't solve the power flow.?
Can't the Matpower take the connected part of the network only and do
load flow for that part? 


Thanks in advance. 


Sridhar Chouhan.

   



function [baseMVA, bus, gen, branch, areas, gencost] = mycase
%CASE9    Power flow data for 9 bus, 3 generator case.
%   Please see 'help caseformat' for details on the case file format.
%
%   Based on data from Joe H. Chow's book, p. 70.

%   MATPOWER
%   $Id: case9.m,v 1.7 2007/09/17 16:07:48 ray Exp $

%%-----  Power Flow Data  -----%%
%% system MVA base
baseMVA = 100;

%% bus data
%         bus_i     type        Pd      Qd      Gs      Bs      area    Vm      
Va      baseKV  zone    Vmax    Vmin
bus = [
            1       3       0       0       0       0       1       1   0       
12.47     1     1.1     0.9;
            2       1       3.3100      1.7874  0       0       1       1       
0       12.47     1     1.1     0.9;
            3       1       2.1300  1.1502      0       0       1       1       
0       12.47     1     1.1     0.9;
            4       1       2.5600  1.3800  0       0       1       1   0       
12.47     1     1.1     0.9;    
            5       1       0.9300  0.5022  0       0       1       1   0       
12.47     1     1.1     0.9;
            6       1       0       0       0       0       1       1   0       
12.47     1     1.1     0.9;
            7       1       0       0       0       0       1       1   0       
12.47     1     1.1     0.9;
            8       1       2.0700  1.1178  0       0       1       1   0       
12.47     1     1.1     0.9;
            9       1       2.4200  1.3064  0       0       1       1   0       
12.47     1     1.1     0.9;
            10      1       1.2600  0.6804  0       0       1       1   0       
12.47     1     1.1     0.9;
            11      1       0       0       0       0       1       1   0       
12.47     1     1.1     0.9;
            12      1       1.3300  0.7812  0       0       1       1   0   
12.47     1     1.1     0.9;     
            13      1       5.3400  2.9884  0       0       1       1   0       
12.47     1     1.1     0.9;
            14      2       0       0       0       0       1       1   0       
12.47     1     1.1     0.9;
            15      1       2.6700  1.4418  0       0       1       1   0   
12.47     1     1.1     0.9;
            16      1       0       0       0       0       1       1   0       
12.47     1     1.1     0.9;
            17      1       0       0       0       0       1       1   0       
12.47     1     1.1     0.9;
            18      1       2.6700  1.4418  0       0       1       1   0       
12.47     1     1.1     0.9;
];

%% generator data
%       bus     Pg      Qg      Qmax    Qmin    Vg      mBase   status  Pmax    
Pmin
gen = [
        1       0       0       100     -100    1       100     1       100     
0;
        14      3       0       20      -20     1       100     1       10      
 0;

];

%% branch data
%       fbus tbus r        x    b          rateArateBrateC      ratio   angle   
status
branch = [
        1       2       0.0500  0.5760  0       250     250     250     0       
0       1;
        1       5       0.1270  0.9200  0       250     250     250     0       
0       1;
    1   13      0.1039  0.1700  0       150     150     150     0       0       
1;
        2       3       0.1090  0.1170  0       150     150     150     0       
0       1;
        2       7       0.0010  0.1100  0       300     300     300     0       
0       0;%S1
        3       4       0.1085  0.7200  0       150     150     150     0       
0       1;
        3       8       0.0010  0.1100  0       250     250     250     0       
0       0;%S2
        4       9       0.0010  0.1100  0       250     250     250     0       
0       0;%S3
        5       6       0.0132  0.0161  0       250     250     250     0       
0       1;
        6       7       0.0101  0.0085  0       250     250     250     0       
0       1;
    6   11      0.0010  0.1100  0       250     250     250     0       0       
0;%S4
        6       18      0.0010  0.1100  0       250     250     250     0       
0       0;%S6
        7       8       0.0390  0.1070  0       150     150     150     0       
0       1;
        8       9       0.0220  0.5860  0       300     300     300     0       
0       1;
        9       10      0.0119  0.1080  0       150     150     150     0       
0       0;
        10      11      0.1085  0.1720  0       250     250     250     0       
0       0;
        11      12      0.1023  0.1625  0       250     250     250     0       
0       0;
        12      15      0.0010  0.1100  0       250     250     250     0       
0       1;%S5
    13  14      0.0320  0.2161  0       250     250     250     0       0       
1;
    14  15      0.2032  0.1161  0       250     250     250     0       0       
1;
    14  16      0.2032  0.1161  0       250     250     250     0       0       
1;
        15      17      0.2001  0.2850  0       250     250     250     0       
0       1;
    16  17      0.0010  0.1100  0       250     250     250     0       0       
0;%S7
        17      18      0.1170  0.2920  0       250     250     250     0       
0       1;
        
];

%-----  OPF Data  -----%%
%% area data
areas = [
        1       5;
];

%% generator cost data
%       1       startup shutdown        n       x1      y1      ...     xn      
yn
%       2       startup shutdown        n       c(n-1)  ...     c0
% gencost = [
%       2       1500    0       3       0.11    5       150;
%       2       2000    0       3       0.085   1.2     600;
%       2       3000    0       3       0.1225  1       335;
% ];
gencost=[];
return;