Hi Xiwen, I found a few issues with the data file, but was still not able to duplicate the results of the paper exactly.
- your values of R and X for the branches are off by a factor of 100 (both the
paper and MATPOWER use p.u.)
- branch 2-3 X value was still off by factor of 10
- bus 12 and the branch connecting it are not necessary, MATPOWER handles
multiple gens per bus
- technically, the loads should be entered as dispatchable loads (negative
generators), but since none of the nodal prices are over 200, none will be
curtailed and the solution will be identical
With these changes I get the following for DC OPF ...
================================================================================
| Generator Data |
================================================================================
Gen Bus Status Pg Qg Lambda ($/MVA-hr)
# # (MW) (MVAr) P Q
---- ----- ------ -------- -------- -------- --------
1 1 1 1000.00 0.00 30.64 0.00
2 2 1 800.00 0.00 30.64 0.00
3 3 1 0.00 0.00 30.64 0.00
4 4 1 1864.41 0.00 30.64 0.00
5 5 1 1262.01 0.00 30.64 0.00
6 6 1 1081.72 0.00 30.64 0.00
7 7 1 571.51 0.00 30.64 0.00
8 8 1 1220.34 0.00 30.64 0.00
9 9 1 1500.00 0.00 30.64 0.00
10 10 1 1500.00 0.00 30.64 0.00
11 11 1 700.00 0.00 30.64 0.00
12 11 1 0.00 0.00 30.64 0.00
-------- --------
Total: 11500.00 0.00
... and for AC OPF ...
================================================================================
| Generator Data |
================================================================================
Gen Bus Status Pg Qg Lambda ($/MVA-hr)
# # (MW) (MVAr) P Q
---- ----- ------ -------- -------- -------- --------
1 1 1 1000.00 5.61 31.55 0.00
2 2 1 800.00 9.10 30.98 0.00
3 3 1 0.00 55.56 32.72 0.00
4 4 1 1850.45 8.28 30.50 0.00
5 5 1 1258.95 3.38 30.61 0.00
6 6 1 1112.57 5.28 31.08 0.00
7 7 1 599.49 7.93 31.09 0.00
8 8 1 1195.87 21.78 30.35 0.00
9 9 1 1500.00 -30.41 29.68 -0.00
10 10 1 1500.00 -20.60 29.76 -0.00
11 11 1 700.00 15.98 31.93 0.00
12 11 1 51.45 15.98 31.93 0.00
-------- --------
Total: 11568.78 97.86
So, unfortunately, I'm not sure what is different between this case and the one
in the paper. The base case solution in the paper looks like an AC OPF
solution, since the lambdas are not identical, so it could be related to
parameters not shown in the paper (voltage limits, generator VAr limits, etc.).
However, my guess is that there is a typo somewhere, either in the author's
MATPOWER file or in the paper ... unless, of course, there's still one in your
data file that I missed.
--
Ray Zimmerman