When the OPF does not converge, the result is often meaningless. Finding the 
reason for unfeasibility can be a non-trivial task. Start by checking that 
total fixed load lies between the sum of PMIN and the sum of PMAX for the 
on-line generators. Try removing all of the line flow limits. Try a simple 
power flow with what you think are reasonable voltage and real power set points 
for the generators.

Once you find a feasible OPF solution you may be able to modify parameters 
gradually toward the infeasible case to determine which constraints bind and 
then conflict.

Hope this helps,


-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Apr 22, 2013, at 2:19 PM, angelina sirri <[email protected]> wrote:

> Dear Dr Zimmerman,
> I am doing reliability study in case24_ieee_rts and I have put extra 
> expensive generators in load buses, in order to calculate the load 
> curtailment.I did acopf but for some hours opf did not converged and I saw 
> that the Qmin and max limits were violated.I couldn't find why, So I tried to 
> do dcopf and now, it does not converges again and I see that the extra 
> generators that I have put, some hours generate negative power of small value 
> (like -0,0025).Have you got any idea why is this happening or what should I 
> check??
> 
> Regards,
> Angelina

Reply via email to