There isn’t a really easy to solve what you want with the current version of 
MATPOWER, but I think it should be possible to do it with a few “tricks”.

For a branch between bus X and bus Y ...

1. Add two dummy buses X’ and Y’ and reconnect the line to X’ and Y’ instead of 
X and Y.
2. Add dummy generators at X, X’, Y and Y’ with PMIN = –M, PMAX = M, where M is 
some value larger than the max flow on the line (even in the relaxed solutions).
3. Add user-defined linear constraints to enforce equality between the Pg of 
dummy gen at X and -Pg of dummy gen at X’, and likewise for dummy gens at Y and 
Y’.
4. Set the cost on each of the dummy generators to a piecewise linear function 
that is zero up to the original line limit value, and some large value above 
that.
5. Add user-defined linear constraints to enforce equality between the voltages 
(magnitudes and angles) at X and X’ and at Y and Y’.
6. Remove or relax the original line limit on the line itself.

I don’t think I’ve never tried this, so I’d be interested in hearing how well 
it works if you decide to attempt it.

-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853  USA
phone: (607) 255-9645

On Sep 23, 2014, at 5:51 AM, Jiazi Zhang <jzhan...@asu.edu> wrote:

> Dear all,
> 
> I'm running AC OPF using Matpower for my project and for some cases, the OPF 
> does not converge due to the capacities of several branches are not enough. 
> I'd like to relax the thermal limit constraints on these branches with large 
> penalty factors. But the power flow thermal limit constraints are nonlinear 
> for AC OPF. I wonder if it is possible to do such branch limit relaxation in 
> AC OPF program.
> 
> Best Regards,
> Jiazi    
> 
> -- 
> Jiazi Zhang
> Research Assisant
> School of Electrical, Computer & Energy Engineering
> Ira A. Fulton Schools of Engineering
> Arizona State University
> jzhan...@asu.edu