Positive values for PG, QG in the gen struct represent power injected into the 
bus.

Shri

From: Marco Barbetta 
<marco.barbetta1...@gmail.com<mailto:marco.barbetta1...@gmail.com>>
Reply-To: MATPOWER discussion forum 
<matpowe...@list.cornell.edu<mailto:matpowe...@list.cornell.edu>>
Date: Mon, 24 Nov 2014 17:22:59 +0100
To: MATPOWER discussion forum 
<matpowe...@list.cornell.edu<mailto:matpowe...@list.cornell.edu>>
Subject: Re: Represent generators as PQ buses

Thank you for your clear answer: as you said, i set the 150/20 kV transformer 
as slack bus (because i need to know its P and Q, in order to look for any 
inversion of power towards HV network), and all other buses as PQ buses 
(because i need to know voltage magnitude after running the power flow).

What about the values of PG and QG? Can i keep their "normal" positive values 
or i need to change their signs?

Thank you again,

Marco Barbetta

2014-11-24 17:12 GMT+01:00 Abhyankar, Shrirang G. 
<abhy...@mcs.anl.gov<mailto:abhy...@mcs.anl.gov>>:
Marco,
   MATPOWER does not have any in-built rule that changes the status of a bus 
from PQ to PV if a generator is incident on it. If you have a generator 
declared in the GEN struct with its bus type set to PQ in the BUS struct, then 
the bus voltage magnitude and angle are the variables for the power flow 
solution. For a PV bus, the voltage magnitude is held constant and the angle is 
the variable.

   You need to have atleast one reference bus in your system. If there is no 
slack bus, MATPOWER uses the first bus declared with type PV as the reference.

Shri

From: Marco Barbetta 
<marco.barbetta1...@gmail.com<mailto:marco.barbetta1...@gmail.com>>
Reply-To: MATPOWER discussion forum 
<matpowe...@list.cornell.edu<mailto:matpowe...@list.cornell.edu>>
Date: Sat, 22 Nov 2014 18:50:30 +0100
To: <MATPOWER-L@cornell.edu<mailto:MATPOWER-L@cornell.edu>>
Subject: Represent generators as PQ buses

Dear collegues,

starting from this discussion 
(https://www.mail-archive.com/matpower-l@cornell.edu/msg03439.html) i see that 
is possible to represent generators as PQ buses.

As Simone said in previous discussion, this is requested in order to analyze 
the network's voltage profile, letting voltage magnitude imposed only in the 
slack bus and free to change in all other buses.

My question is: if i put in the GEN struct all generators with their PG and QG, 
in the BUS struct all loads with their PD and QD and i impose bus type = 1 (PQ) 
for ALL buses, will MatPower have any problem? In this way, wil the voltage 
magnitude for all buses be let free to change, in order to be analyzed 
post-simulation? I don't understand if the generator buses automatically become 
PV buses only for the fact to be set in the GEN struct, or if "rules" the 
condition set in the BUS struct.

Another question: in this concept, PG and QG can remain positive or have to be 
set with negative values?

Thanks to all.

Best regards,

Marco Barbetta